I had a load of bedding in the tumble drier (condenser type if that helps) this morning and noticed it had stopped working. It is plugged into the mains via an extension lead and the plug from the machine had partially melted on the surface and it is stuck in the extension lead. I popped another plug on the power cable and dug out another extension lead and all is working again.
However, I am surprised at how this could have happened – we have a modern consumer unit with RCDs and it was fully tested when we had some work done a couple of years ago so I am surprised it didn't trip that rather than just melt the plug and blow the fuse. Fortunately no damage has been done (other than to the plug and extension lead) but should this be expected?
Posted : 25/11/2024 3:14 pm
pictonroad, nobtwidler, pictonroad and 1 people reacted
Sounds like a lucky escape ?
I didn't understand, do you mean the heat of the machine melted it? Or the wiring in the plug overheated and melted the plug?
Posted : 25/11/2024 3:17 pm
J-R, roger_mellie, roger_mellie and 1 people reacted
RCDs test leakage, they don't test bad connections causing heat.  An arc fault detection device(AFDD) might have tripped, but these are only currently recommended, but are seldom fitted.
Posted : 25/11/2024 3:24 pm
Murray, leffeboy, 10 and 3 people reacted
Was the plug pushed all the way in?  If not, then I think they can get much hotter than usual and over time the material they are made of degrades
Posted : 25/11/2024 3:25 pm
J-R, chakaping, chakaping and 1 people reacted
Is your extension lead fully unwound?
It should be for the sort of draw a tumble drier will need. But it's not an appliance I'd ever run off an extension lead.
And how is ventilation around the machine? And I'm assuming it's regularly de-fluffed! 🙂
Posted : 25/11/2024 3:27 pm
doris5000 and doris5000 reacted
 mert
Don't they get really funny about high load devices using extensions anyway, and a slightly dodgy wobbly plug is going to add to any issues. (or even a perfectly healthy plug!).
Posted : 25/11/2024 3:28 pm
andy4d and andy4d reacted
Likely a poor connection between the plug and the extension lead. The tumble drier will be pulling close to max current for a UK plug so you need a good connection. Extension lead isn't ideal, at the very least make sure it is a good quality one not an ebay/poundland special, but really you want a proper socket near the appliance.
As above, I wouldn't expect a failure like that to trip an RCD, its not what they are detecting.
J-R, 10, 10 and 1 people reacted
The plug was fully pushed in and extension lead fully unwound. I don't really have mean option not to run off an extension lead but it goes without saying that we have never had this issue before. Ventilation is okay, but I am going to move it to somewhere where it has more space around it.
Here's an image of it... (and yes, a lucky escape but we never run the machine when we are in bed or out of the house for this very eventuality).
Posted : 25/11/2024 3:34 pm
integra and integra reacted
Faulty plug?  Poor contacts on the fuse?  Its a moulded on plug or otherwise I would think it dodgy connection where the wires are screwed in to the terminals in the plug.
As above4 could well be a poor connection in the plug to extension lead creating arcing and thus heat
Posted : 25/11/2024 3:53 pm
Given what has happened (and the fact I need to run the drier off an extension) I was looking at replacing the extension lead with one of these...
Thoughts please.
And I’m assuming it’s regularly de-fluffed!
Ohh yes – that is a guilty pleasure of mine and I get disappointed if my wife gets to de-fluffing before I do!
Posted : 25/11/2024 4:07 pm
My guess is the problem is the extension lead as they can be cheap with poor connections.  The connections will then heat up and you are seeing the result of that heat being conducted up the prongs of plug.  I would be replacing both the cable (which you did) and the extension lead with something a bit meatier
edit: I don't know the brand of extension that you linked to but given that it is a single socket at the correct power rating it is likely to be ok.
Posted : 25/11/2024 4:10 pm
b33k34 and b33k34 reacted
 poly
I don’t really have mean option not to run off an extension lead
Of course you do (in order of preference):
- get a sparky to install a proper socket near the drier.
- replace the whole cable from the drier
- put a good "joint" in the cable rather than an extension lead (I would use an outdoor rated one because areas with driers are often damp = corrosion = heat.
I'd be inquisitive enough to take a hacksaw to that plug and extension lead to try and understand what caused the heat.  By any chance does that extension lead sit somewhere that gets a lot of vibration (like on top of a washing machine?).  That's not to imply that I've never bodged a solution with an extension lead - but there is always a way if you are sufficiently motivated.
Here’s an image of it… (and yes, a lucky escape but we never run the machine when we are in bed or out of the house for this very eventuality).
Always puzzled by people who say that like being in your house when it catches fire is better than being out - I get it might mean it gets contained but unless you have a smoke detector in this space (utility? kitchen? garage?) and a fire door on the space that you religiously keep closed when indoors then I'm not convinced you'll be better off.  You noticed this because it didn't work - not because of the smell of burning plastic.
Posted : 25/11/2024 4:12 pm
silvine, trail_rat, trail_rat and 1 people reacted
 Yak
Yes, something heavy duty with a high current rating and not something wound up. I have done the same when I forgot my heavy duty extension and ran some redhead lights (photo stuff) off an old extension reel. That melted too and caused a stink. I think I was in the V&A and was lucky not to set off their smoke alarm. Anyway, better than a heavy duty extension will be to get a proper socket in the correct location.
Posted : 25/11/2024 4:16 pm
That extension isn't BS1363. The body isn't wide enough, you could get the Earth pin in upside-down and expose the live socket. Throw it away and get one not made out of finest Chinesium.
Posted : 25/11/2024 4:18 pm
b33k34, mattyfez, andy4d and 9 people reacted
The problem is the extension lead.
The socket has melted due to poor connections to the extension leads socket.
This can even happen in ordinary sockets when loaded up continuously by things like tumble driers. Usual advice there is use an MK branded socked.
Ideally, you’d eliminate the extension lead and get a single gang socket fitted by a pro. I work in the fire industry and know any of us will tell you not to use an extension lead, but…
If you must, buy a masterplug extension like This (links to screwfix). Don’t buy any safety critical electrical equipment from Amazon, they have absolutely zero checks that the stuff they sell is up to basic, mandatory standards (see electric bike fires…)
Posted : 25/11/2024 4:19 pm
andy4d, rumbledethumps, GlennQuagmire and 3 people reacted
Never run a dryer off an extension lead - get a new socket fitted. You were lucky!!!
Posted : 25/11/2024 4:22 pm
mattyfez, andy4d, andy4d and 1 people reacted
Thoughts please.
That doesn't look much better. It claims to be BS1363/A - I think it's lying. As a rule of thumb it's best to avoid Amazon brands which look like they've randomly pulled a handful of Scrabble tiles.
Posted : 25/11/2024 4:24 pm
I posted a coupl eof posts ago with something I found - I assume that would be suitable?
Posted : 25/11/2024 4:26 pm
Posted : 25/11/2024 4:27 pm
That has nothing to do with ventilation.
andy4d, goldfish24, andy4d and 1 people reacted
I posted this same issue last year.
Mine was the dryer next to the socket and in theory moisture could have been getting on the socket. I changed the socket and try not to have tumble on at same time as washing machine, no issues since
I can’t recall exactly but I think some of the wires in the plug were slightly loose
Posted : 25/11/2024 4:28 pm
mildbore and mildbore reacted
I work for consumer safety, but not the fire brigade side. Fires are not my thing. Avoiding issues in the first place, yes, that's what I advise on as a job. Just reading your first story made me feel sick. And then you replace the plug, and start all over again with a new extension?? FFS, get a sparky in and put a proper socket in for the job. Please don't die.
Posted : 25/11/2024 4:32 pm
hightensionline, andy4d, hightensionline and 1 people reacted
Never plug high power devices into extension sockets.
Even a kettle, for example can pull 3 kilowatts. Albiet only for 3 mins at a time, it's a massive load..
Call a sparky.
Posted : 25/11/2024 4:38 pm
andy4d, crewlie, andy4d and 1 people reacted
Yes, to identify the cause of the machine stopping working – and I'm now on here asking further advice. The problem is that the power lead for the machine is really short (barely longer than the height of the machine) and I can't get a proper socket fitted as it would have to be above a sink which would fail regs The washing machine that sits under it plugs into a double socket under the sink but the drier cable isn't long enough.
Posted : 25/11/2024 4:43 pm
I've had a couple of melted plugs and sockets from charging my EV. Putting 13A through cheap eBay electricals (and dodgy domestic wiring in a damp conservatory) for an extended period can do that regardless of nominal ratings.
These days I've turned it down to 10A and have also replaced the cheap smart wifi timer socket for a solid 30A job. Still plugged into the wall via a (fairly robust) consumer plug and extension cable. And it's a drier chunk of wall.
Posted : 25/11/2024 5:02 pm
"the power lead for the machine is really short" - so why not get a longer cable fitted to the tumble drier?
Posted : 25/11/2024 5:16 pm
How about something like this – then join up with some more mains cable (I have some high-rated stuff)?
I could do that I guess – I just assumed it wouldn't be very easy to access but I could take a look.
Posted : 25/11/2024 5:28 pm
Dryers/washing machines / dishwashers and ovens are  usually on a spade terminal under a flap at the back of the machine.  Crimping / soldering a new spade terminal to take 3kw will be the next point of failure. As others have said, I’d try and get a sparky in to fit new socket.
Posted : 25/11/2024 5:38 pm
But a new socket isn't possible - it is as close as regs allow (due to there being a sink) but it is, annoyingly, about 6 inches too far away (ironically, this was fitted by our electrician and the previous tumble drier mains cable reached). There is nowhere else I can place the tumble drier without wholesale changes to the layout of the utility room.
Posted : 25/11/2024 6:12 pm
This has a good plug and sock but at 10 metres the length then potentially becomes the issue, as I guess the OP would most likely have to coil it.
https://www.brennenstuhl.co.uk/en-GB/selection-of-themes/safety/why-you-should-always-unwind-a-cable-reel-completely-and-untangle-an-extension-cable-completely
Posted : 25/11/2024 6:31 pm
^ Correct, I realised that after I posted. Shortest similar one on screwfix is 5m.
You can avoid coiling by laying it in longer lines, back and forth. Maximise the area of the coil and avoid circularity. Reason is to avoid magnetic induction heating the cable.
I’ve pondered recommending instead extending the cable using 32A rated wagos fitted inside a wago box, and using 3093Y flex as the extension, thereby avoiding the plug and socket extension. But not sure I can recommend that.
Replacing the machines flex with a longer one is of course an ideal option, but it needs doing well. IME they’re not on screw terminals on the back like an oven, IME tumble driers have a captive flex which will be terminated internally with crimps. I’d not particularly trust a jobbing appliance repair person to do it well, but it’s an option to consider.
Posted : 25/11/2024 6:39 pm
Get a sparky to fit a longer cable to the tumble dryer?
Posted : 25/11/2024 6:43 pm
slight hijack but related - I have an electric flymo that  has a nicked cable which I want to replace.  Ideally I would like to increase the length of the lead at the same time as this will enable the mower to reach the corner of the garden from one socket, rather than having to switch sockets half way through the mow.
Is there a maximum length of cable? Currently have circa 8 metres
ta
Posted : 25/11/2024 6:45 pm
@kormoran
Just get a 25m extension lead for that. That's what I use for all my gardening and outdoor electrical tool needs! 🙂
https://www.screwfix.com/p/masterplug-ldct2513bq-4-xd-13a-4-gang-25m-cable-reel-240v/54615
Posted : 25/11/2024 7:05 pm
Isn’t the dryer under a bench? I thought if the space was encapsulated it could be  right under a sink and still be within the safe zone? (Like most dishwasher installations in a new build).
Posted : 25/11/2024 7:16 pm
It's designed like that for the current drawn, although it's possibly over-cautious. A longer cable of the same conductor size won't correlate with the current and may overheat; the longer it is, the worse it gets.
A long cable tends to get coiled when the machine is pushed back to the wall, making things worse. Heat behind a tumble dryer will worsen this. Don't just stick an extension lead in there
Over-heating at the plug/socket may be the terminations being loose or otherwise poor.
A BS1362 fuse should deal with overcurrent, but they can be notoriously slow to blow, taking several minutes in some circumstances at much higher currents than nominally rated
Bottom line. Get proper advice, the solution might be as simple as a 6" longer new cable with a new plugtop
Posted : 25/11/2024 7:38 pm
johndoh and johndoh reacted
The drier is above the washing machine on the counter-top. Annoyingly, if there wasn’t a wall unit in the way, the mains cable would reach (it currently has to wrap around the side and bottom of the unit.
Posted : 25/11/2024 9:05 pm
Jesus christ, no, stop it! Is your photo and others not a wake-up call that bodging it is a really bad idea?
Out of the gate, you've cut the plug off so you're stuck with a shorter cable. You either need a closer power socket, for which you (demonstrably) will need an electrician, or you need to replace the entire cable in one stretch from inside the guts of the machine for which you will likely require an appliance technician - with all due respect, from what you've posted here I wouldn't trust you to wire the plug. If the power socket is too near the sink, other sides of the appliance may be available?
Or I suppose, you never run it when you're out of the house, so you could save a few quid and then when the house burns down you'll all be in it so it will no longer matter. You could put the money you've saved towards a will or life insurance.
Seriously mate, I know I'm being sarky for comic effect but do it properly. Please. If nothing else, I'll feel like a right **** for writing that if you do burn the house down. Think of the Cougar.
Posted : 25/11/2024 9:50 pm
integra, GlennQuagmire, integra and 1 people reacted
Surely from an H&S perspective you're going to get a proper charger fitted aren't you......
Posted : 25/11/2024 10:18 pm
I don't believe I'm suggesting this but, could you go through the unit? That's what mine does, I have washer | cupboard | dryer, the plug socket is at the back of the cupboard and there's a hole in both side walls to pass the cables through. They're blanked off with the cable management covers you get on the tops of desks. If I'm underestimating your DIY skills, you'd only need a small hole now that there's no plug.
Posted : 25/11/2024 10:26 pm
Are you sure that the tumble drier is functioning normally? It's probable that poor contact to a cheap extension lead caused your issue. But also possible that the machine has an intermittent fault.
Posted : 25/11/2024 10:34 pm
so the cables too short to barely reach the length of the the machine.
but the socket that it would need would be over a sink.....
how on earth is this tumble drier in a safe space with regards to the sink ?
Posted : 26/11/2024 8:30 am
but the socket that it would need would be over a sink…..
Because the extension lead is routed away from the sink. It's pretty normal to have electrical items next to sinks (see also dishwashers). Both my under-sink cupboards have power outlets in them for just this reason.
Posted : 26/11/2024 9:15 am
 mert
The plate for my drier and washer is 6 foot up the wall above/behind the washer and drier. Cables all in a nice sturdy conduit.
A conduit that basically runs under the sink, through two units, past the central heating and into the distribution/fuse box.
Posted : 26/11/2024 9:40 am
 poly
Does a socket not only have to be 300mm from a kitchen/utility sink? Given dryer will be 600mm how is it impossible to put a socket behind the dryer in a position that conforms to the rules?  It may just be we aren’t understanding the room layout.
Posted : 26/11/2024 10:14 am
nickjb and nickjb reacted
This thing about not using extension leads for appliances. Does that include dishwashers? Asking for a friend.
Posted : 26/11/2024 1:55 pm
 Yak
Have a look at the current draw/ power requirements. Probably similar to most tumble driers, but not a heat pump tumble drier which will be lower. So best not to use an extension for a dishwasher and get a dedicated socket so you can use the provided short lead.
Posted : 26/11/2024 2:09 pm
Extension leads are only really suitable for a temporary fix, and even then they're not suitable for all appliances, certainly not for high-load (3kW) devices, ie those that have a resistive heating element. The whole point of Table H7 in the BS7671 On-Site Guide is to recommend enough sockets in specific rooms to ensure extension leads are not used. If they are used long-term it's an indication that the wiring infrastructure is unsuitable, and should be adapted to suit. It will not be difficult, and shouldn't be too expensive, to adapt the wiring to provide an additional socket that is suitable for a permanent connection for the TD and will give you peace of mind that it won't fail, but you do need to have the work done by a reputable tradesperson.
If you're looking to have an electrician in to do the work it may be worth asking them to fit AFDDs too.
Yes.
IAAE
Posted : 26/11/2024 2:11 pm
Cougar2, andy4d, Cougar2 and 1 people reacted
What if a tumble drier is situated in a bathroom less than 3 metres across?
Posted : 26/11/2024 2:37 pm
 zomg
I'm waiting for the first poster to proclaim they've wired their washing machine to the house via an isolator because they no longer trust plugs or sockets.
Posted : 26/11/2024 2:41 pm
 mert
Have a look at the current draw/power requirements
This is really the killer, anything continually pulling over about 75% of your maximum load on a circuit would be unsuitable for using an extension on, and the higher the load/longer the extension the greater the risk.
I'm even in the process of rewiring a couple of sockets all the way back to the fuse box to make doubly sure that they will withstand 16A continuous. (They already should, technically, but it's 30 year old wiring).
Posted : 26/11/2024 2:43 pm
 poly
pretty sure UK regs don’t allow a socket within 3m of a shower or bath.  Not sure if you can permanently wire an appliance in a bathroom as I have seen some washing machines - but of course not everyone sticks to the regs.
Posted : 26/11/2024 2:55 pm
mick_r and mick_r reacted
You could in previous editions of the regs so it's quite likely that you've seen legal installations
We're now on the 18th Edition and I'm no longer up to date
Posted : 26/11/2024 3:32 pm
On the photo of the plug it clearly says "fused" .  That's just to avoid the swear filter on here.
Posted : 27/11/2024 1:12 pm
Cougar2, cogglepin, cogglepin and 1 people reacted
I've opened a few extension leads to replace the cord. Some of them are shocking, bent bits of thin steel clipped down the body making questionable contact with the pins. Dump the extension and just put a longer cable on the dryer, and use a decent heavy rubber cord for 13a
Posted : 27/11/2024 4:00 pm
So I ended up going to my local electrical trade-counter and asked their advice – I got one of these - rated for a 20amp load, a decent plug and a short length of twin and earth all for £5.11, wired it up last night and all seems fine. This time I have pinned it up to the underside of the wall units that are sited above so it is well out of the way.
Posted : 28/11/2024 1:52 pm
leffeboy and leffeboy reacted
In a bathroom??? .........is it placed next to the toaster and kettle as well?
Posted : 28/11/2024 1:56 pm
Huh? Why not? There is no external wall in my kitchen so nowhere to put the vent hose.
Posted : 28/11/2024 4:24 pm
Lucky escape for sure OP. Went to a dryer fire near to you last night and they were not so lucky and probably won’t be spending Christmas at home this year.
Posted : 28/11/2024 5:03 pm
Plenty vent free options. Has been for 15 years.
Zone rating isn't optional just because it's inconvenient for you.
Posted : 28/11/2024 5:38 pm
They also show a "CE" mark on the plug. Plugs shouldn't have a CE mark. and it's not even a CE mark, it's a China Export mark designed to look like a CE mark. It is completely meaningless
https://www.kimuagroup.com/news/differences-between-ce-and-china-export-markings/
Posted : 02/01/2025 4:48 pm
Murray and Murray reacted