Posts: 41642
Free Member
 

So I’m hearing that a bigger rad would help? It’s possible, there’s not a ton of room here but I could go 50% larger probably.

You could also change the type of radiator, more panels/convectors within the same length.

IANAE.

If your flow temp is 60°, you’ll never see 70° in the tank and the tank stat will just keep calling for more heat, no?

Also, Arguably you only need your tank hot water at 60-65 for Legionella pasteurisation so theres some saving to be made by reducing the temperature you store HW at and making the thermal gradient smaller.

That's what I was aiming for, except the boiler just as a dial labeled min->max, so I'm going to have to get a thermometer out to measure the return temps. I'd presumed though it would just shut down when the load was low ( Tin + minDt -> Tout > Tset).

Trying to figure out how to set it up this winter, I'd thought of getting some Tado valves + controller for the most used rooms. But then that means I'll need to leave at least the hallway* on dumb all the time one of them is calling for heat which seems pointless. The alternative is to go all in on the Tado system and do every radiator so they an call for heat individually and nothing needs to be always on?

*current system is thermostat and timer in the hallway and that rad turned upto max which allows me to turn off the towel rail in the bathroom which would otherwise be the 'always on' bit.


 
Posted : 03/10/2022 12:51 pm
Posts: 2737
Free Member
 

I've had to open the door in the garden office to let the heat out.
It needs a couple of minutes with the fan heater first thing to take the chill off, then warms up lovely during the morning with the sun coming through. Even on overcast day it warms up enough to not need heating.
The wife and dog have joined me down here today


 
Posted : 03/10/2022 12:52 pm
Posts: 1555
Full Member
 

Turned the heating on on 1st October. Boiler pissed itself and was promptly turned off. Plumber just been out. Various bits relating to the capture, storage and disposal of condensate now on order and won't be here for days. Sadly, the small fortune being saved on gas is going on boiler parts next week. Costing effing money even when switched off!!


 
Posted : 03/10/2022 1:08 pm
Posts: 91000
Free Member
 

That’s what I was aiming for, except the boiler just as a dial labeled min->max, so I’m going to have to get a thermometer out to measure the return temps.

I just found that the manual for mine states the temperature range on the knob which is from 30 to 82C.

I'd turned it down to half way then turned up the hot water thermostat in the tank. The boiler fired for a bit then cut out, and the display indicated that the 'desired' temperature had been reached. This suggests that the burner just goes on and off, and the knob doesn't actually reduce the flame.


 
Posted : 03/10/2022 2:53 pm
Posts: 91000
Free Member
 

But then that means I’ll need to leave at least the hallway* on dumb all the time one of them is calling for heat which seems pointless. The alternative is to go all in on the Tado system and do every radiator so they an call for heat individually and nothing needs to be always on?

Same situation as me. Apparently if you fit a bypass valve (or already have one) then you can do the all-smart-TRV system. The risk if you have all the rads shut off apparently is burning out the pump, because the water won't flow. But I cannot see how no water at all flows, because the rads aren't in series with each other? Unless the last rad is in series with the loop that feeds all the others? I need a circuit diagram of the plumbing.


 
Posted : 03/10/2022 2:56 pm
Posts: 18073
Free Member
 

I’d turned it down to half way

Try minimum and maximum settings (30 and 80). On my boiler there were two burner levels, on the minimum it was definitely on the slower burner and on max logically enough the higher burn. Somewher between the it transitioned but without trying the extremes you won't know if you have two burner levels or just one. An added complication is that on the boiler I had the central heating circuit and hot water circuit had independant controls so running hot water could be made to activate either the higher or lower level of burn irrespective of what the central heating was doing. Fitting a shower head with a finer jet meant I could adjust it so it never go onto the higher burn for a shower.


 
Posted : 03/10/2022 4:45 pm
Posts: 11605
Free Member
 

@mattyfez good link, realised I've already been reading their website.

Another video worth watching that was mentioned in yours:


 
Posted : 03/10/2022 5:18 pm
Posts: 0
Free Member
 

Turned the heating on on 1st October. Boiler pissed itself and was promptly turned off.

I'm half expecting that when it gets cold enough to turn on. Maybe it would be worth a turn on and bleed the rads just in case we need it at some point.


 
Posted : 03/10/2022 6:01 pm
Posts: 0
Free Member
 

Didn't twig that running HW and Ch together would drive it into high burn mode. Have just changed the timings in the morning to keep them separate. Probably bad science practice by changing multiple things at once but I'm trying to get a mode of operation that is efficient. Fingers crossed it all works. The MVHR system I am designing should go a way to help distribution of localised heat. Just need to find a way to make heat with spare solar leccy for the underfloor heating. Ideas welcome.


 
Posted : 03/10/2022 6:35 pm
Posts: 790
Free Member
 

any thoughts on what the most efficient way of running underfloor heating?. we have an electric (as opposed to water) system for a garden room. A combination of an impossibly difficult to set up timer and a pretty slow to make itself known to the user nature means that we have tended to leave it on at a lowish level rather than go for periodic heating cycles - is that the best way forward even if it means consumption at peak times?


 
Posted : 03/10/2022 6:41 pm
Posts: 11605
Free Member
 

@blackhat that video I posted above should help answer your question.


 
Posted : 03/10/2022 7:07 pm
Posts: 15068
Full Member
 

@squirrelking

Blimmin heck, thats going to take some digesting, hahah!


 
Posted : 03/10/2022 7:11 pm
Posts: 91000
Free Member
 

Ah, my burner does seem to be variable after all. I tweaked the knob whilst it was running and it revs up or down on an apparently sliding scale.

I've turned the hot water up to 60. I don't think we have Legionnaire's disease in the house but there might be other nasties hanging around in there. I may insulate the airing cupboard with some boards on the walls and door to keep the heat in.


 
Posted : 03/10/2022 7:17 pm
Posts: 11605
Free Member
 

Blimmin heck, thats going to take some digesting, hahah!

Yeah, there is a bit of maths used to justify the theory but it looks sound enough to me. You don't really need to understand that bit IMO, just the conclusions.


 
Posted : 04/10/2022 8:23 am
Posts: 4439
Full Member
 

Jesus wept ive just got he predicted costs for this winter. bills going u 3 to 4 fold!!


 
Posted : 04/10/2022 11:15 am
Posts: 17728
Full Member
 

molgrips

Same situation as me. Apparently if you fit a bypass valve (or already have one) then you can do the all-smart-TRV system. The risk if you have all the rads shut off apparently is burning out the pump, because the water won’t flow.

Didn't you say previously on this thread that you have some towel radiators without TRVs? If that's the case, then as long as you don't close the lockshield valves on these rads, then they act as your bypass valves.
This is how the radiator in our bathroom is set-up (and I think it's quite standard), so there's an flow bypass built-in.

We stuck the heating on last Thursday in the evening; mainly because the towels in the bathroom weren't drying (might have to investigate a towel radiator with electric functionality, so we can pop it on when the heating is off) at some point.
It was on for an hour and the house got too hot (thermostat on 19, now reduced by a degree).
Since then, we had 30mins on Fri, 15mins on Sat and apart from that it's not come on again.

I am looking into other options for the winter when I am working from home. We don't have a smart set-up, and I don't want the entire house being heated when we could restrict it to my small office.
How do the costs of an oil-filled radiator stack-up compared to having the boiler running to heat the whole house? I'm guessing it would be cheaper, but need to do the sums.


 
Posted : 04/10/2022 11:38 am
Posts: 91000
Free Member
 

Didn’t you say previously on this thread that you have some towel radiators without TRVs? If that’s the case, then as long as you don’t close the lockshield valves on these rads, then they act as your bypass valves.

Yes, and also hallway rads, but they are dumping heat into the hallways and bathrooms that I don't want to heat cos I'm not in there. Ok so the bathrooms will need some heat to dry them out and the hanging towels etc, but not hallways.

might have to investigate a towel radiator with electric functionality, so we can pop it on when the heating is off

You can get hybrid towel rails that are like HW ones but also have an electric heating element. I want some of those because towels still need drying in the summer.

How do the costs of an oil-filled radiator stack-up compared to having the boiler running to heat the whole house?

Well, our boiler is 12kW I just found out. An oil rad to heat one room is what, 2kW? So there's 6x the heat output. The boiler isn't 100% efficient but in theory and ideal conditions it is close, being a condensing boiler. That's 6x the output, but at 8p/kWh vs 50p for my electricity, that's about the same. So you'd have to decide if the boiler was on for the same amount of time as the radiator. To be honest, it sounds pretty comparable.

You could also consider that gas might be 6x cheaper but it could be heating more than 6x the volume.


 
Posted : 04/10/2022 12:03 pm
Posts: 0
Free Member
 

Ok so the bathrooms will need some heat to dry them out and the hanging towels etc, but not hallways.

Dry air is more efficient .. unless the moisture has somewhere to go from the bathroom


 
Posted : 04/10/2022 12:07 pm
Posts: 17728
Full Member
 

molgrips

Well, our boiler is 12kW I just found out. An oil rad to heat one room is what, 2kW? So there’s 6x the heat output. The boiler isn’t 100% efficient but in theory and ideal conditions it is close, being a condensing boiler. That’s 6x the output, but at 8p/kWh vs 50p for my electricity, that’s about the same.

I am not sure the calculation is as easy as that, is it?
Our boiler is 30kw, but looking at the manual it says that CH output is fully modulating from 6.1 to 24.2KW, while for hot water it can fully modulate up to a max of 30.3kw. (Our boiler was serviced today, so i had already dug the manual out).
So presumably, it isn't always pumping out 24.2kw when the heating is on although I don't know how it determines where to run within that output range? Max output with larger delta T, and then reduced output as delta T approaches set T, to avoid over-shoot?
Dunno.
Not a lot of info about this kind of thing on the Ideal website although just found a couple of articles on other sites I will read while eating my lunch.


 
Posted : 04/10/2022 12:31 pm
Posts: 13916
Free Member
 

8p/kWh vs 50p for my electricity, that’s about the same.

Why is your electricity 50p/kwh?

The cap seems to have set it at about 35p/kwh.


 
Posted : 04/10/2022 1:33 pm
Posts: 11605
Free Member
 

Yes, and also hallway rads, but they are dumping heat into the hallways and bathrooms that I don’t want to heat cos I’m not in there.

@molgrips check that video above that I posted, it makes a very good argument (technically and economically) against isolating individual rooms unless they are remote or insulated form teh rest of the house.


 
Posted : 04/10/2022 1:40 pm
Posts: 41642
Free Member
 

Didn’t you say previously on this thread that you have some towel radiators without TRVs? If that’s the case, then as long as you don’t close the lockshield valves on these rads, then they act as your bypass valves.
This is how the radiator in our bathroom is set-up (and I think it’s quite standard), so there’s an flow bypass built-in.

Yes also, but we never use the main bathroom, we've got an en-suite where the towel rail is on the HW circuit. So if we close don't close the valve on that it's heating a room with no one it it. Instead I've set the TRV in the hallway to max (~28ish?) so it never closes before the thermostat on the wall (19C) has switched the boiler off.

Bypass valve seems to be the right tool for the job.


 
Posted : 04/10/2022 2:34 pm
Posts: 4420
Free Member
 

Why is your electricity 50p/kwh?

The cap seems to have set it at about 35p/kwh.

I'm not Molgrips, but I'm with Good Energy, which is one of the companies exempt from the cap. As of this month, what GE are terming 'The Government Energy Price Guarantee' will kick in. Our unit costs will now be

Gas 12.6p
Electricity 49.7p

I knew that going with a renewable energy provider would be a bit more expensive, but....ouch

Fortunately we're a low-use household so even at those prices we shouldn't be much over £200 a month. But still... I'm not a high earner! And this hurts!


 
Posted : 04/10/2022 2:37 pm
Posts: 0
Free Member
 

Heatings on full blast. The f****s have over £800 of MY MONEY in their bank account and cant/wont refund it, so Im just going to spend it for them - oh! and they put up my direct debit by £20. I get the uplift in direct debit, but trying to get that much money back from them has proved to be a total nightmare as you just cant get through (Scottish power). So at current prices I should get a week of 20C then its back to cuddling up with the dog and the cat.


 
Posted : 04/10/2022 2:40 pm
Posts: 91000
Free Member
 

So presumably, it isn’t always pumping out 24.2kw when the heating is on although I don’t know how it determines where to run within that output range?

Presumably by varying the burner heat output based on the return flow temp. I'm not sure mine does this, but it seems like such an obvious thing to do I can't imagine why it wouldn't.

I need to go back through the manual.

EDIT this is getting a bit silly now and I'm sure any plumbers are laughing their heads off, but I've found out that boilers can be modulating, whereby they do vary the burner according to the heat demand which must be measured as I said by the inlet temperature. This article says that a modulation ratio of 1:6 is average for a modern boiler i.e. it can vary between say 5 and 30kW, but in my manual it says it only varies between 9.3 and 12kW which is shit. But this may be a function of it being small.

Heatings on full blast. The f****s have over £800 of MY MONEY in their bank account and cant/wont refund it, so Im just going to spend it for them

That's daft. Just cancel the DD for the next 4 months or whatever it is.


 
Posted : 04/10/2022 2:51 pm
Posts: 91000
Free Member
 

Why is your electricity 50p/kwh?

Octopus standard variable tariff. 16p 12am-7am, 41p at other times. I'm assuming that's ex vat.


 
Posted : 04/10/2022 3:03 pm
Posts: 91000
Free Member
 

A couple of interesting points from that video, relating to me:

1. The graph he shows of boiler efficiency vs load - this is another picture of the same thing:

Given that my boiler has such poor modulation* it cannot run at less than 77% load so would revert to being an on-off boiler, and that could drop the efficiency off a cliff. My radiator is only rated at 780W, so even at max power that would represent about 8% of the minimum modulating output so that would mean at most less than 50% efficiency and the boiler would be cycling on and off all the time. Conversely, from the graph a proper modulating boiler would be quite happy at that load and maybe even near peak efficiency.

2. Our house deviates a lot from the theoretical house in his example (which he does acknowledge, to be fair). Where I sit all day is on the top floor and is always much warmer than the kitchen two floors below where it's coldest. That said, point 1 above means that heating only this room on gas with my current boiler is a non-starter. I could well be better off with an electric rad.

3. I could still go for smart TRVs, but only to turn the rooms a bit during the day. So it'd save some but not tons.

4. I really need to figure out what the boiler is doing when it's heating the house and the hot water. Turning the output down manually will increase the efficiency, but if I go below 60 I can't heat the hot water to the sanitary temperature. This is presumably why better boilers have two outputs. And if the hot water is on, and the bottom of the tank is nearly at 60 but the boiler output temp is nearly at 60 then it won't dump much heat out of the heating coil and the return temps won't be very low. So again I might be better off heating with electricity overnight. I'll try and invest in some sort of temperature probes for the in and out pipes.

5. My heating design is utterly shit. There are a hundred or so houses on this street, I bet no-one else has thought about it in this level of detail. They're probably all on the original boilers and will be chucking tons of money away. Not because the boiler itself is nominally inefficient but because the systems haven't been well designed or configured.

* The modulation is specified as being between 9.3kW and 12kW but it also says the output temperature can be as low as 30. Does this mean that it reverts to on-off mode if you specify a really low temp? I think it probably does.


 
Posted : 04/10/2022 3:44 pm
Posts: 17728
Full Member
 

@molgrips ...have a read of this online article I found earlier

HeatGeek link

Your boiler does sound very small for a 3-storey (presumably 3 or 4 bedroom?) house. That will be partly because you have a tank, so are not having to heat water 'on-demand'.

From that article - yes, the degree of modulation will vary based on the size of the boiler & smaller ones can't modulate as much.
And yes - it will cycle on & off to simulate a lower modulation level if needed (like PWM control for LEDs etc).

Regarding the set temperatures - yeah, our boiler (Ideal Logic Max C30) has two temp dials - one for HW & one for CH.


 
Posted : 04/10/2022 4:45 pm
 ctk
Posts: 1811
Free Member
 

 
Posted : 04/10/2022 4:53 pm
 ctk
Posts: 1811
Free Member
 

Worth watching!


 
Posted : 04/10/2022 4:54 pm
Posts: 41642
Free Member
 

* The modulation is specified as being between 9.3kW and 12kW but it also says the output temperature can be as low as 30. Does this mean that it reverts to on-off mode if you specify a really low temp? I think it probably does.

Presumably it's intended to run nearly flat out until all the rads are upto temperature and it senses that the return temp reaches it's set point (or when modulated to it's minimum the outlet temp is over the set point, effectively the same thing).

Looking at that graph unless you had all smart TRV's (or turned 90% of the house off) then I can't see how any system would drop to ~10% load for very long. Presumably in our 'dumb' systems the heating comes on and takes a while to heat up ~10 radiators, then they start switching off at the TRV, 9,8,7,6, which speeds up as the boiler is now sending it's full power to fewer rads, 5,4,3,2,1 then switches off. Being able to run at 10% load would only work if the heating was on 24/7 so the demand at any instant was only a small amount for one room at a time. And I doubt you'd recover that last 5-10% efficiency Vs extra lost heating the house all day.

Also:
That graph ignores the 3rd axis which would be the water set point temperature, it'll obviously be more efficient to run a boiler with a higher temperature differential to the water (both in the radiative and condensing sections).


 
Posted : 04/10/2022 4:59 pm
 irc
Posts: 5188
Free Member
 

I googled my boiler as a matter of interest. Worcester GreenStar 400. Output varies from Max 30Kw down to 3Kw.

https://www.worcester-bosch.co.uk/professional/products/boilers/greenstar-4000

It was fitted in July and replaced a 40 year old Baxi. Hardly used the heating mode yet but using approx half the gas for hot water. New boiler Combi - heat on demand - old boiler - hot water tank. Interesting to see the winter bills. Though better controls and doubled loft insulation will play a part as well so savings won't be purely the new boiler.


 
Posted : 04/10/2022 5:37 pm
Posts: 11269
Full Member
 

Not putting the heating on – how’s it going…?

Turned air source heat pump off in January so no central heating/hot water. Been doing fine as it’s not been that cold, although I have a multi fuel stove in living room so obviously that’s fired up in the afternoon and loaded up at night, tiny 1bedroom bungalow so it’s ok at the moment. Got my electricity use down to an average of 2.5kw a day or £1.15 ish or 850kw/year. If I ran the air source heating/hot water It uses near enough 4000kw/year according to previous bills due to non insulated and draughty housing association bungalow so nope…….not using it.


 
Posted : 04/10/2022 5:51 pm
Posts: 9201
Full Member
 

My bastard smart heating system has been smart enough to stop my heating from turning on. Got elderly relatives arriving today so spent an unpleasant hour at lunch pairing thermostats to RF receiver (again), uninstalling and reinstalling app (again) and linking Wi-Fi up (again).


 
Posted : 04/10/2022 6:01 pm
Posts: 7915
Free Member
 

I googled my boiler as a matter of interest. Worcester GreenStar 400. Output varies from Max 30Kw down to 3Kw.

Mine is a Greenstar 4000, but its only 15kw because I'm running a system boiler because I like to have a tank. The benefit is the new circuit controls and integral pump are covered in the warranty now too, and because its all managed by the boiler it should in theory help with efficiency.

AFAIUI, modulation is achieved by the gas valve. The new greenstars can modulate every 10%. The previous ones were 50% or 100%.


 
Posted : 04/10/2022 7:09 pm
Posts: 0
Free Member
 

Starting to think we should bin off our boiler (put in by the previous owner in 2017 and underpowered) and fit a modulating one with more headroom. With underfloor heating going in and a larger tank fitted this year the existing one is not the best*.
After about a week of having the dial turn down to about 40% from about 80, the water in the tank is noticeably cooler which is subsequently making us use more hot water. I was going to turn the temp up a touch on the tank to make it go further but as we are now not even reaching the current setpoint.....

*We need to move it anyway. A replacement should allow us to make better use of our heat generation.


 
Posted : 05/10/2022 8:34 am
Posts: 2010
Full Member
 

I didn't use my Central heating until November 1st last year. So hopefully I'll manage to make it beyond that date this year.


 
Posted : 05/10/2022 10:38 am
 IHN
Posts: 19694
Full Member
 

All this talk of boilers is just about gas-fired ones, anyone got any tips for optimising an oil-fired one? It's brand-spanking new, one of these:

https://www.worcester-bosch.co.uk/products/boilers/directory/greenstar-danesmoor-external


 
Posted : 05/10/2022 10:48 am
Posts: 6513
Full Member
 

What's all this talk of modulation and condensing? Our 35year Stelrad Ideal Sprint is still going strong. It might not be as efficient but it's easily fixable (don't worry I don't touch the gas side) and parts are still available.
Thankfully our main heat source is a Greta approved massive Coalbrookdale Stove thats been lit a few times recently.
[url= https://i.ibb.co/XLbX5LF/B4047948-593-F-457-E-906-E-73577-FD3434-E.jp g" target="_blank">https://i.ibb.co/XLbX5LF/B4047948-593-F-457-E-906-E-73577-FD3434-E.jp g"/> [/img][/url]
[url= https://i.ibb.co/869Dxb9/B6-DD5-D21-AB4-F-48-A0-8-B98-C8-C64-A146717.jp g" target="_blank">https://i.ibb.co/869Dxb9/B6-DD5-D21-AB4-F-48-A0-8-B98-C8-C64-A146717.jp g"/> [/img][/url]
[url= https://i.ibb.co/c6kh4hZ/DAB3-CDEA-6-B73-46-E8-8-DE3-883-E033-C966-F.jp g" target="_blank">https://i.ibb.co/c6kh4hZ/DAB3-CDEA-6-B73-46-E8-8-DE3-883-E033-C966-F.jp g"/> [/img][/url]


 
Posted : 05/10/2022 12:53 pm
Posts: 91000
Free Member
 

I had an idea.

I've now learned I need my boiler output temp on a lower value for more efficiency due to the boiler itself, the size of the rads and the fact I have a well insulated house in a mild location. But I also am now concerned about bacteria in the HW tank and with a low temperature from the boiler I might not be able to get the water hot enough.

So I think I will set the water temp to a modest value, but use the immersion heater on a timer just before the off-peak period ends to get it nice and hot. I've just switched to an EV tariff with 7.5p/kWh overnight charging, that will make it fairly cheap. I think the immersion heater has a fixed temperature of 60C or something sanitary.


 
Posted : 05/10/2022 3:50 pm
Posts: 15068
Full Member
 

I think I read you can go as low as 50c in a tank before bacteria etc. becomes an issue? Don't quote me though.

The tip in one of the vids about having the hot water as cold as possible is better, as there's no point having a red hot, hot water pipe, only to mix it with cold at the tap/shower as your're just cooling down the water you've just paid to heat up.

I run my hot water at 40c, as that's hot enough without requiring much, if any mixing with cold at the business end.
That's also as low as it will go, but I don't have a hot water tank, so don't need to worry about bacteria as much.


 
Posted : 05/10/2022 4:00 pm
Posts: 41642
Free Member
 

So I think I will set the water temp to a modest value, but use the immersion heater on a timer just before the off-peak period ends to get it nice and hot. I’ve just switched to an EV tariff with 7.5p/kWh overnight charging, that will make it fairly cheap. I think the immersion heater has a fixed temperature of 60C or something sanitary.

That's how most electrically heated homes do it. And TBH makes sense if you've got a tariff that makes the gas and eclectic rates the same.

I think I read you can go as low as 50c in a tank before bacteria etc. becomes an issue? DOn’t qoute me though.

I run my hot water at 40c, as that’s hot enough without requitring much if any mixing with cold at the buniss end.
That’s as low as it will go, but I don’t have a hot water tank so don’t need to worry about bacteria as much.

It's probably fine, I'm sure there's something in building regs though that says it has to reach 50C at the tap, but if it's a thermostatic mixer it has to be lower at the outlet. And the tank has to reach 60C at least once a day.


 
Posted : 05/10/2022 4:00 pm
Posts: 1187
Free Member
 

I run my hot water at 40c,

so don’t need to worry about bacteria as much.

Just around body temperature- yum.
Even without a tank that’s a recipe for building a lovely biofilm inn the pipe work. As above, wants to be much hotter to prevent growth. Appreciate that it’s not potable water, but adding the aerosol from a shower head it’s not ideal. HSE advise 50c or higher on hot water distribution systems. Of course if the pipe runs are long then would want hotter at the source to allow for heat loss.


 
Posted : 05/10/2022 4:40 pm
Posts: 4170
Free Member
 

as there’s no point having a red hot, hot water pipe, only to mix it with cold at the tap/shower as your’re just cooling down the water you’ve just paid to heat up.

The point is to have any hot water that is stored at 60ºC, to avoid legionella. Then mix it with cold at the point of use to avoid scalding.

The total energy is the same, if you want 10 litres of water at 40º, whether you heat that 10 litres from 20º to 40º or heat 5 litres to 60º and mix it with 5 litres at 20º.


 
Posted : 05/10/2022 5:26 pm
Posts: 41642
Free Member
 

The total energy is the same, if you want 10 litres of water at 40º, whether you heat that 10 litres from 20º to 40º or heat 5 litres to 60º and mix it with 5 litres at 20º.

In an isentropic system it would be, but nothing is isentropic.


 
Posted : 05/10/2022 5:37 pm
Posts: 18073
Free Member
 

Assuming you've got a closed system and no open header tank with birds and bats shitting in it then there are a number of points to consider:

Mains water is chlorinated and the residual chlorine by the time it reaches your home will deal with pipes and and tanks that get a regular fresh dose. The danger areas are dead end pipes and unused tanks, legonaires loves them - they get neither fresh chlorinated water nor sufficient heat to kill the bugs.

My hot water is solar, it only gets over 60° in Summer and over 50° on really sunny days in Spring. It's currently running in the 40s. Am I worried? No, the water is replaced regularly. However, if I go away for a few weeks in Autumn or Winter and the water is left to stagnate then I use the immersion heater to get it properly hot and then run hot water through all the pipes in the system.


 
Posted : 05/10/2022 5:52 pm
Posts: 91000
Free Member
 

The tip in one of the vids about having the hot water as cold as possible is better, as there’s no point having a red hot, hot water pipe, only to mix it with cold at the tap/shower as your’re just cooling down the water you’ve just paid to heat up.

Yes, but you use less of the water at the tap when it's hotter. I think the reason to have the hot water tank cooler is that you lose less heat. We turned it right down in the hot weather (the tank temp, which dictates when the hot water system shuts off - not the boiler outflow temp) because it contributes to making the top floor of the house hot. And if the water tank is 45 and the boiler outflow temp is 70 then it'll heat up the water tank more efficiently and give a nice cool return temp at the same time.

However, if I go away for a few weeks in Autumn or Winter and the water is left to stagnate then I use the immersion heater to get it properly hot and then run hot water through all the pipes in the system.

Interesting. Still, the immersion heater might end up a bit cheaper. But perhaps not if it's hitting 65C versus 50C from the gas. Hmm.

The total energy is the same, if you want 10 litres of water at 40º, whether you heat that 10 litres from 20º to 40º or heat 5 litres to 60º and mix it with 5 litres at 20º.

Yeah but your whole tank is at 60 versus 40, and a tank at 60 loses more heat than a tank at 40.


 
Posted : 05/10/2022 6:07 pm
Posts: 2191
Free Member
 

Heating still not on here; bar one hour when I tested it for operation last week after doing a radiator bleed. We both run fairly hot bodies as it is so we might last out another couple of weeks unless it takes a plunge outside.

Re: hot water, I've tried storing ours at 50C versus storing it at 60C, and having it on to heat all through the day and night rather than just an hour in the morning and a few hours at night. it made so little difference i decided to just go with 60C as it meant we got more out of one tank and weren't left a bit short after two showers and washing the dishes in the space of a couple hours.


 
Posted : 05/10/2022 7:36 pm
Posts: 32265
Full Member
 

Seem to have hit the time of year when it's too cold to dry your towel on the line and not cold enough for the radiators to come on


 
Posted : 05/10/2022 7:43 pm
Posts: 2010
Full Member
 

My neighbours hang out their washing on cold days as long as there is a breeze that is capable of drying out the ground. They don't own a tumble dryer. They do have a drying rack that winches up to the ceiling in their kitchen.


 
Posted : 05/10/2022 8:09 pm
Posts: 9093
Full Member
 

Goes to check, hot water tank at 55c, has been for years. Needs to be hot, but not enough to scald.


 
Posted : 05/10/2022 8:21 pm
Posts: 0
Free Member
 

Seem to have hit the time of year when it’s too cold to dry your towel on the line and not cold enough for the radiators to come on

@morecashthandash Wholly agree. Shower in the morning. Then a cool shower after a ride or gym. By that time, the towel is nowhere near dry yet.

Maybe a first-world problem. But it can't be good hygienically if your towel never actually dries completely.


 
Posted : 05/10/2022 8:41 pm
Posts: 94
Free Member
 

Heating not on here yet - it's felt a bit cool and the thermostat in the hall has dropped as low as 17.5 so far this Autumn

I'd normally have a small electric heater out for a small bit of heat in individual rooms, but I've held off for now

If I'm on the couch watching TV I have a small blanket to put round my legs - works nicely


 
Posted : 05/10/2022 8:48 pm
Posts: 7751
Free Member
 

All that's required for stuff on a clothes line is dry wind; no warmth necessary.
Returning to the topic - I'm wearing t-shirt, overshirt, shorts, shearling lined slippers and that won't change for several weeks; heating fired up once a week to purge system.
Will be using local (council owned) gym - which is within walking distance - more to maximise the benefit to me; that includes showers.
Energy bills aren't a consideration for me but improving fitness and getting showers subsidised by the locals - can't turn that down!
Having said that, it's shit for far too many.


 
Posted : 05/10/2022 10:10 pm
Posts: 6312
Free Member
 

Aga went on yesterday.

Drying rack above it back in action!

Heating still off hopefully running to November before I put it on


 
Posted : 05/10/2022 10:23 pm
Posts: 1617
Full Member
 

I mind my mum hanging my clothes out on the line in the snow, I think she was aiming for freeze dried. How I laughed when I bent feet into my jeans and stood them up.

Windy and no rain, the washing is out.


 
Posted : 05/10/2022 10:48 pm
Posts: 39449
Free Member
 

Our heating ticked on this morning before we got up as evidenced by the radiators being warm to the touch.

it certainly wasn't on for long as the rads are warm to touch but still fairly cool.

Good to know it still works since I cleaned out the baffles and turbulator


 
Posted : 06/10/2022 7:47 am
Posts: 91000
Free Member
 

A little bit parky this morning in the kitchen. My first thought was 'ooh heating on' but then I put on jumper, problem solved.

Going to go round and get rid of some draughts this weekend.


 
Posted : 06/10/2022 9:55 am
Posts: 13594
Free Member
 

The tip in one of the vids about having the hot water as cold as possible is better, as there’s no point having a red hot, hot water pipe, only to mix it with cold at the tap/shower as your’re just cooling down the water you’ve just paid to heat up.

We have a "pencil" hot water tank so tiny volume, hence to have an acceptable quantity of hot water for showers, we have to run the HW tank thermostat at 75C in winter, I suspect the top of the tank is closer to 80C. I had to fit thermostatic mixer valves to the hot water taps as otherwise you can scold yourself on them!


 
Posted : 06/10/2022 9:59 am
Posts: 32265
Full Member
 

Lovely morning sun coming in our south facing windows.

Meanwhile, in the north facing "office" I've resorted to a blanket over my legs for the first time this year


 
Posted : 06/10/2022 10:46 am
Posts: 41642
Free Member
 

Still off here, just reaching the point where it's slightly chilly in the morning/evening, but realistically no colder than it would be later in the year with the heating on then going off before bedtime, or just not doing nay more than taking the edge off it in the mornings.


 
Posted : 06/10/2022 10:49 am
Posts: 11884
Full Member
 

First day I've worked from home for a couple of weeks. It's been a bit bloody parky until I've turned on the oven to desiccate some liver dog-treats! Fair play to SWMBO's 1 and 2, there's been no moaning about having the heating on or sneaky boiler adjustment this autumn.

Not sure we'll be holding out too much longer and we have built up some credit in the account over summer.


 
Posted : 06/10/2022 1:10 pm
Posts: 4656
Full Member
 

wore two layers for warmth for last night's bike ride. First time this autumn (with the exception of wearing a waterproof in rain)

pyjama t-shirt has also re-appeared this week.

heating still off.


 
Posted : 06/10/2022 1:53 pm
Posts: 4324
Full Member
 

It’s cold now so heating on, I don’t like being cold and the washing wasn’t drying.

Put the floor on in the bathroom too, think I’ll have to reduce the temperature and time a bit on it. Apparently uses about 600W when it’s heating.

On the plus side my gas has gone down from 6p to 5.74p - small wins.


 
Posted : 06/10/2022 10:07 pm
Posts: 11884
Full Member
 

Well, 8 hours after my previous message I caved and turned it on. Flow temperature set to 3 as apparently that's most efficient. I didn't know that before, always assumed MAX POWER would be best.


 
Posted : 06/10/2022 10:18 pm
Posts: 233
Free Member
 

Not even thought about putting the heating on. But then I'm sat outside a bar in Girona in t shirt and shorts😀


 
Posted : 06/10/2022 10:26 pm
Posts: 2010
Full Member
 

On the plus side my gas has gone down from 6p to 5.74p

Who's that deal with? That's near enough half the energy price cap.


 
Posted : 06/10/2022 10:48 pm
Posts: 4324
Full Member
 

@retrorick with Octopus, we have Go for car charging.

It’s their gas tracker, I think it has the potential to go up to the cap. It was 4p earlier in the year.

[img] [/img]


 
Posted : 06/10/2022 11:25 pm
Posts: 7751
Free Member
 

LoL @ pete68


 
Posted : 07/10/2022 12:09 am
Posts: 13330
Full Member
 

Heating still not on here in the Midlands, and I hung washing up outside yesterday that dried perfectly well.
Still got the summer duvet on the bed as well.


 
Posted : 07/10/2022 8:48 am
Posts: 91000
Free Member
 

I hung washing out inside because showers are forecast here. Heating's not on, let's see how fast it dries and if the house gets too cold.


 
Posted : 07/10/2022 9:52 am
Posts: 13594
Free Member
 

I hung washing out inside because showers are forecast here. Heating’s not on, let’s see how fast it dries and if the house gets too cold.

We do that in summer if it's raining, often open the windows and stick a fan pointing at the washing - dries very quickly. In winter, we switch on the dehumidifier and shut it in the spare bedroom - dries overnight.


 
Posted : 07/10/2022 10:22 am
Posts: 91000
Free Member
 

Quite windy here which should help evict the humidity from the washing. But it is feeling somewhat chilly in my room. I'm going to put a jumper on and my thick socks. Is it due to the wind or the humidity from the washing?


 
Posted : 07/10/2022 11:12 am
Posts: 0
Free Member
 

still resisting here (Bromley - S/E London) but looking at the 2 week weather forecast its gradually trending down so i can't see us lasting until the end of the month before caving in.


 
Posted : 07/10/2022 11:17 am
Posts: 20561
Free Member
 

I haven't once felt remotely cold yet (and my wife has only commented that she is getting a bit chilly once) so I am hoping to hold out for some weeks yet. I am also thinking about getting some larger rugs to cover up the tile floors in the bathrooms so we don't need the underfloor heating on.


 
Posted : 07/10/2022 11:19 am
Posts: 9093
Full Member
 

Heating is on, hour in morning and about the same early evening, but set at 17.5c. Gas consumption now around 20Kwh - a day, or about £2.50 a day. That will most likely double to 40KWh in the colder months (looking back to Feb when I started logging useage). What would have been a £60 per month bill, is likely to be nearer £150.


 
Posted : 07/10/2022 11:22 am
Posts: 7167
Full Member
 

Tested the log burner for the first time. Yep, they get hot. Took longer than expected at around 40mins from ignition to chucking out a decent warmth but once its up and running, very happy
My newly acquired wood is mostly 14 to 16% moisture and takes a flame really well. Burnt 1 builder bucket of split 6in lengths in the evening.
Need to keep an eye on the daytime temps, and when its single figures prep the stove so i can light it as soon as I get in from work.


 
Posted : 07/10/2022 12:13 pm
Posts: 119
Free Member
 

No heating on in Costa del Chorley yet. Blankets, shutting off unused rooms, have insulated the garage door which is integrated into the house (big difference!). Want to enquire about fitting a wood burner, but it's a new build house and unsure if it's allowed etc. Also 6 solar panels on the roof which I want to see if I can convert somehow to also heat the hot water tank


 
Posted : 07/10/2022 1:14 pm
Posts: 40225
Free Member
 

Just flicked the oil-filled rad on in the office.

Been having a cheeky 20 mins or so of that now and then, plus the odd couple of hours of the CH when there's people over.

Sitting here in home office wearing big hoody, fleece-lined trews and hat on.


 
Posted : 07/10/2022 1:18 pm
Posts: 91000
Free Member
 

Gas consumption now around 20Kwh

Is it my maths or is that a hell of a lot?

I'm on about 1/4 of that I think in a 3 bed house. Is yours big and draughty?


 
Posted : 07/10/2022 1:25 pm