[Closed] Help... radiator changed in ensuite, now got a walk in fridge...

60 Posts
26 Users
0 Reactions
167 Views
Posts: 0
Free Member
Topic starter
 

Maybe someone can help here... We had our ensuite completely changed around, and although it LOOKS great, it just won't get snuggly warm any more 🙁

Here is the NEW layout - the radiator is now just as you walk in on the left; it is a nice shiny chrome towel radiator, the output acoording to the spec sheet is definitely enough (more than!) for this small room, but it just won't get warm!

[img] [/img]

Previously the radiator was on the wall to the right of where the shower is now; it was an old white towel radiator style one, and it heated the room no problem.

Is it the radiator? I read on the web (must be true...) that chrome ones don't heat a room as well as non-chrome ones?
Or the location of the radiator? Or cause the walls are now tiled it will always be a colder room??

Any ideas welcome...


 
Posted : 03/02/2016 2:30 pm
Posts: 17728
Full Member
 

First thing is the radiator getting as hot as the old one? Is there a cold region at the top that might indicate trapped air, which can be easily resolved by bleeding the radiator?

It could be that the lockshield valve on the radiator (normally under some kind of cap at the bottom of the radiator) is closed more than the previous one was, restricting flow through the radiator & so there isn't as much heating effect taking place?
EDIT - to open the lockshield valve, pull the cover/cap off and use some pliers to turn it anti-clockwise. Half a turn to start with & see if that helps.

Do you cover the radiator in a towel? My Wife does this and wonders why the bathroom doesn't get warm.

Is the door normally kept shut? If not, the heat might be just escaping into the neighbouring room.


 
Posted : 03/02/2016 2:36 pm
Posts: 0
Free Member
 

Presuming you've checked the rad is filling correctly and doesnt need bleeding or anything?


 
Posted : 03/02/2016 2:36 pm
Posts: 41642
Free Member
 

Is the radiator actually getting hot?

No idea why, but my towel radiator has stopped working. We removed, cleaned and replaced all the radiators in the house except the towel rail. Refilled and bled everything. Now everything is much hotter, except the towel rail. Before it would get warm to about halfway up (needed a bleed obviously), no nothing.


 
Posted : 03/02/2016 2:36 pm
Posts: 17728
Full Member
 

thisisnotaspoon - Member

Is the radiator actually getting hot?

No idea why, but my towel radiator has stopped working. We removed, cleaned and replaced all the radiators in the house except the towel rail. Refilled and bled everything. Now everything is much hotter, except the towel rail. Before it would get warm to about halfway up (needed a bleed obviously), no nothing.

Much better flow through the rest of the system now means that the towel radiator isn't getting it's share of flow?
Is it getting warm at all? Was the system re-balanced with the new radiators?


 
Posted : 03/02/2016 2:39 pm
 wool
Posts: 21
Full Member
 

Faulty valve at the bottom. Just had the same problem here had to drain it down and replace them both.


 
Posted : 03/02/2016 2:42 pm
Posts: 8177
Free Member
 

Is it covered in towels......? 😉


 
Posted : 03/02/2016 2:45 pm
Posts: 3327
Free Member
 

No idea why, but my towel radiator has stopped working. We removed, cleaned and replaced all the radiators in the house except the towel rail. Refilled and bled everything. Now everything is much hotter, except the towel rail. Before it would get warm to about halfway up (needed a bleed obviously), no nothing.

You need to re-balance your system (i.e. each radiator).


 
Posted : 03/02/2016 2:51 pm
Posts: 20561
Free Member
 

Do we know yet if the rad is actually getting warm?

If the BTU output says x then it means x, not y when taking into account it is chrome.

Edit - is the door left open when the room isn't in use? If so, much of the heat will be leaving the room through the adjacent door...


 
Posted : 03/02/2016 2:54 pm
Posts: 13916
Free Member
 

I read on the web (must be true...) that chrome ones don't heat a room as well as non-chrome ones?

🙄


 
Posted : 03/02/2016 2:55 pm
Posts: 0
Free Member
Topic starter
 

Thanks for all the suggestions!

Should have said that the radiator does get hot, and was bled a few times (had other new radiators installed in kitchen and system was drained).

We tried it with and without towels on; it did not heat the room any better without towels. The old radiator was always covered in towels and seemed to be okay...

The system was not rebalanced when the final new radiator was installed, but would that matter if the radiator is getting hot?


 
Posted : 03/02/2016 2:55 pm
Posts: 0
Free Member
Topic starter
 

I read on the web (must be true...) that chrome ones don't heat a room as well as non-chrome ones?

Yes, I know 🙂

Oh, and the door to the adjacent room is shut. Although maybe I should keep it open, that room does get nice and warm 😀


 
Posted : 03/02/2016 2:57 pm
Posts: 20561
Free Member
 

Is it just that the new room is colder (ie, more tiles etc)?


 
Posted : 03/02/2016 3:08 pm
Posts: 20561
Free Member
 

And what is the output of the new radiator compared to the old one?

For example, if the room measurement says you need a 600BTU and you got an 800BTU one then it should get warm enough (when balanced correctly) however if your old radiator was rated at 1600BTU then the new one isn't going to compare.


 
Posted : 03/02/2016 3:11 pm
Posts: 13192
Free Member
 

just put a jumper on. 😀


 
Posted : 03/02/2016 3:19 pm
Posts: 3327
Free Member
 

Should have said that the radiator does get hot

Does it get as hot as the old radiator, or are you just saying it gets warm/hot.

Oh, and the door to the adjacent room is shut.

Does the room get warm if you close the bathroom door?


 
Posted : 03/02/2016 3:19 pm
Posts: 17728
Full Member
 

alp_girl - Member

Thanks for all the suggestions!

Should have said that the radiator does get hot, and was bled a few times (had other new radiators installed in kitchen and system was drained).

We tried it with and without towels on; it did not heat the room any better without towels. The old radiator was always covered in towels and seemed to be okay...

The system was not rebalanced when the final new radiator was installed, but would that matter if the radiator is getting hot?

Based on all of that, I would find the lockshield valve & open it a 1/2 turn. I've been trying to get the baby's nursery to a suitable temperature with regard to the rest of the house, so tweaking things. Even though the radiator was already getting 'hot' the room was very cool, but a half turn on the lockshield valve has sorted it right out a the radiator is definitely hotter.
Worth a try for 2 mins with a pair of pliers.


 
Posted : 03/02/2016 3:21 pm
Posts: 251
Full Member
 

Are you leaving the bathroom door open more so you can admire it's newness as you walk past?

😉


 
Posted : 03/02/2016 3:26 pm
Posts: 4143
Free Member
 

The system was not rebalanced when the final new radiator was installed, but would that matter if the radiator is getting hot?

It may well do

I had a cold rad that was fixed by restricting the flow in another rad 2 floors up (town house

Edit ... sorry not really answered your question.... are you sure rad is still as hot as the old one ...?

If it is .... in the re-fit, any messing about with waste/plumbing that goes out side .... ie has a new draft been created...??


 
Posted : 03/02/2016 3:27 pm
Posts: 0
Free Member
Topic starter
 

Right, the lockshield valve will be the next thing to try, thank you! Managed to turn it 1/2 a turn, which means it's fully open now...

The room gets a bit warmer if we leave the heating on all day, so after ca. 12 hours 😳

just put a jumper on. 😀

Not a bad idea, have a shower with a jumper on and save doing the washing 😛

Guess it's also worth checking whether the old radiator was more "powerful" than the new one...


 
Posted : 03/02/2016 3:44 pm
Posts: 0
Free Member
Topic starter
 

If it is .... in the re-fit, any messing about with waste/plumbing that goes out side .... ie has a new draft been created...??

Well, the wall that the toilet is on is not ceiling height, but has a big dormer window; previously there were some built in cupboards along it, now it's just tiled - maybe that makes a difference, too...


 
Posted : 03/02/2016 3:47 pm
Posts: 20561
Free Member
 

previously there were some built in cupboards along it, now it's just tiled - maybe that makes a difference, too...

Yep that can make a difference as the cupboards may have provided some insulation.


 
Posted : 03/02/2016 3:50 pm
Posts: 41642
Free Member
 

Much better flow through the rest of the system now means that the towel radiator isn't getting it's share of flow?
Is it getting warm at all? Was the system re-balanced with the new radiators?

Shouldn't be, the valve to the towel rail is fully open so if anything should be robbing the rest of the house, and I fitted TRV's to all the other radiators at the same time, so you'd expect the rest of the house to warm up, then the towel rail if it was the last one in the circuit.

Did that deliberately as you're not supposed to do all the radiators with TRV's to prevent the boiler having to pump against a dead head, so the towel rail seemed the obvious one to leave with manual valves.


 
Posted : 03/02/2016 4:26 pm
Posts: 0
Free Member
 

a fundamental point.. it is not a radiator designed to heat a space.. it is a heated towel rail designed to heat a towel drapped over it.


 
Posted : 03/02/2016 6:41 pm
Posts: 20561
Free Member
 

True totalshell, but the original was also a towel radiator....


 
Posted : 03/02/2016 6:43 pm
Posts: 1617
Free Member
 

Chrome ones will lose a bit of the ability to "radiate" heat as the low emissivity of chrome vs a typical not that glossy white will have an effect BUT the term radiator is a misnomer as most heat from a radiator is via conduction to the air giving convective heating in your room.

A covered towel radiator is never going to heat as well as a simple rad due to the towel blocking the air flow and the radiation. In the flat I specced a nice tall, oversized towel rad for this reason and it also means that 2 people can actually use the towel radiator as tbh as far as drying towels go they are pretty useless at that too.

I suspect something else might be amiss if the radiator is pretty much the same size as the old one. You say it's getting hot but is it really getting as hot to touch (be careful) as the other rads?

The comment above about TRVs does not apply to most modern systems as the radiator without the TRV should be in the room with the room stat. An old system with a convection loop might have 2 rads without TRVs as one provides active cooling for the boiler (in our case the bathroom) and then another is the return loop for the system (in our case the landing and stupidly we have a TRV in the kitchen with the room stat so I took it off as the place is rented and not mine to mess with any further).

I would check that the system is definitely bled, close off all but one rad at a time and force the water through and check that the towel radiator is definitely getting the proper flow and EVERY bar is getting hot as it could also be an internal fault with the towel rail that you've not noticed.


 
Posted : 03/02/2016 6:54 pm
Posts: 0
Free Member
 

I have a heated towel rail in my en suite. Its electric and does a great job of stopping the towels going musty and airs the room of moisture. But it doesn't actually create enough heat to warm the room. That's the job of the radiator in there, which has a convection finned and TRV on it. It works well too. Water heated towel rails are great if you leave the heating on, but as soon as the water and heating go off, so does the towel rail. I believe you can fit inline heaters to compensate for the issue, but a towel rail covered in towels is not going to do diddly in warming the room.


 
Posted : 03/02/2016 6:59 pm
Posts: 384
Free Member
 

I don't suppose you had some spotlights fitted too? My electrician removed all the insulation and didn't put it back.


 
Posted : 03/02/2016 7:15 pm
Posts: 0
Free Member
Topic starter
 

Some more good ideas there - maybe the fact that the cupboards are gone and it's now just a tiled wall makes a difference. I also remember that the guys took out insulation from there to get the toilet cistern into the wall, maybe they didn't put enough back in 🙄

As johndoh said, the fact that we had a towel radiator style one in there before, and that it was covered in towels all the time but still managed to heat the room is the thing that I don't understand...

We did have spotlights fitted, but there's plenty of insulation up in the attic. (Your comment did remind me of the other insulation though, see above...)

Luckily we live in balmy Scotland, so only a few frosty nights up here every year 😆 😆


 
Posted : 03/02/2016 8:25 pm
Posts: 0
Free Member
 

Is there a new more efficient extractor fan now? Or has the old one been cleaned in renovations? It's by the door so maybe more draughty now but same temp?

Who knows? You'll get used to it.


 
Posted : 03/02/2016 10:46 pm
Posts: 2642
Free Member
 

The whole system might need re-balancing - the lock-shield valves on the radiators which have had TRVs fitted may well have been shut off and opened again without noting the setting, and the new rads that have been fitted should be balanced into the system. (Does the room with the new rads get nice and warm?)


 
Posted : 03/02/2016 11:19 pm
Posts: 6071
Free Member
 

Has removing the built-in cupboards increased the room volume significantly??


 
Posted : 04/02/2016 6:10 am
Posts: 205
Free Member
 

Is the bathroom in an attic conversion / storey and a half house?
If yes I'd seriously investigate the insulation in the sloping ceiling and behind the vertical coom walls!
The above suggestion re. any extract fan may also be pertinent as it effectively s 100mm dis. open vent.
Other than that it looks to be a very slim (500mm?) towel rail...how tall is it and what's the output


 
Posted : 04/02/2016 6:58 am
Posts: 13916
Free Member
 

True totalshell, but the original was also a towel radiator....

Maybe the original towel rail had a radiator panel in it so it was better for heating?


 
Posted : 04/02/2016 8:09 am
Posts: 0
Free Member
 

Where's the window?


 
Posted : 04/02/2016 9:17 am
Posts: 91000
Free Member
 

In the flat I specced a nice tall, oversized towel rad for this reason

Yep. The lady at Wimpey specced the towel rails for us and said you need much bigger towel rails than you do rads.


 
Posted : 04/02/2016 9:22 am
Posts: 7033
Free Member
 

If its all bled and whatnot and still not heating, my best suggestion is:

put trvs on all the other rads
leave the heating on a lot longer

We have a large chrome towel rail in our small bathroom. Even so, still useless at keeping the bathroom warm - if it wasn't for the fact it is on 24/7 (its the heat leak for the coal boiler).


 
Posted : 04/02/2016 9:27 am
Posts: 91000
Free Member
 

I would suggest keeping all your perishable foodstuffs in the en-suite. You can then turn off the fridge in your kitchen and save money.

FWIW, our towel rail (about 6ft by 2ft6) keeps our en-suite boiling, and has to be turned down almost all the way off.


 
Posted : 04/02/2016 9:44 am
Posts: 0
Free Member
 

Guessing - it's getting hot but not "using" the heat.
Part of balancing the system is ensuring that the hot water has time to drop in temperature leaving the radiators.
It needs to stay in there a while or your boiler will be on and off constantly as it thinks the system is up to temp where the returning water is the same as the outgoing.
Your TRV (if fitted) will shut the rad at whatever temp you have it set to (3 is about 21 degrees)
However you need to be able to ensure that the water is moving slow enough to transfer its heat to the metal of the rad and the air from there.
I was taught to turn the shield valve off.
Then bring it back open slowly listening to the flow noise.
You'll hear it start.
Then you'll hear it decrease the further you open the valve.
If you can't hear it - its open too far.
Close it back off until you hear a good "shhhhhhhh".


 
Posted : 04/02/2016 9:56 am
Posts: 20561
Free Member
 

Is the floor in the room different? If you have gone from (say) vinyl to tile then the room might be the same temperature but will feel much colder as the tiles feel cold underfoot.


 
Posted : 04/02/2016 11:01 am
 teef
Posts: 0
Free Member
 

Heated towel rails are never going to be as good as a radiator at heating a room - the surface area is smaller so they can't transfer the heat to the room as efficiently. If it's always hot that tells you it's not working very well - it should transferring the heat from itself to the room. A mate of mine had a vertical tubular style radiator in his lounge and it was always hot but was useless at heating the room - looked nice though. Replace it with a normal radiator - a device designed to heat space - and your problems should be solved.


 
Posted : 04/02/2016 11:15 am
Posts: 20561
Free Member
 

But teef - they only had a towel radiator before...


 
Posted : 04/02/2016 11:32 am
 teef
Posts: 0
Free Member
 

But teef - they only had a towel radiator before...

Maybe it had a larger surface area than the new one...


 
Posted : 04/02/2016 11:48 am
Posts: 0
Free Member
Topic starter
 

Hello everyone 🙂

Right, I can now confirm the radiator really does get hot, all the way bottom to top. Doing that lockshield valve thing hasn't magically cured the problem though, still quite fridgey in there this morning...

Is the floor in the room different?

There were these tiny tiny square tiles on the floor before (ugh), now we have proper big floor tiles. Could be that they feel a bit colder?

Where's the window?

It's above the toilet (a big dormer one)

hammyuk,
It doesn't have a TRV - does your idea still work with a "normal" valve?

Not sure about the surface area, I never measured the old one; however, going by how the towels fit on it, it can't be that much different (the old one was wider, the new one is higher).

The new one is [url= http://www.bestheating.com/phoenix-ascot-chrome-designer-heated-towel-rail-1600mm-x-500mm.html ]this [/url]one.

FWIW, our towel rail (about 6ft by 2ft6) keeps our en-suite boiling, and has to be turned down almost all the way off.

... but is it chrome 😆 ?

The whole system might need re-balancing - the lock-shield valves on the radiators which have had TRVs fitted may well have been shut off and opened again without noting the setting, and the new rads that have been fitted should be balanced into the system. (Does the room with the new rads get nice and warm?)

The other room with new rads gets very warm... Maybe we really should get the boiler man to come back and balance the system!

Who knows? You'll get used to it.

Sure, but only once I know I've asked on here and that's the conclusion 😉 😉


 
Posted : 04/02/2016 2:49 pm
Posts: 91000
Free Member
 

Right, I can now confirm the radiator really does get hot,

How hot though? On full chat our hottest rads are too hot to hold a hand to for long.

but is it chrome

Of course!

Balancing could be the answer. The ones that are too hot, turn them down. It might also help to figure out which order the rads are moving away from the pump. Our house is three storey, and the bottom's quite hard to keep warm. The hot water goes from the boiler straight up to the top floor then down through the rads to the ground. So the top floor rads were the hottest, which is the opposite of what you want because the heat rises in the first place.

I turned the top two practically off, and installed a much bigger rad in the hall so that most of the heat starts off down there.


 
Posted : 04/02/2016 3:03 pm
Posts: 7033
Free Member
 

Guessing - it's getting hot but not "using" the heat.

If the rad gets to 80 deg (or whatever it gets to) then there is a fixed* amount of heat going from the rad to the room.

Water speed affects return temp into boiler which IIRC affects how fast/slow the boiler cycles + how efficient it runs.

* yes, not quite fixes, varies a bit depending on temperature of room, etc.


 
Posted : 04/02/2016 3:05 pm
Posts: 20561
Free Member
 

Maybe it had a larger surface area than the new one...

Well yes maybe, and that has also been covered 😉


 
Posted : 04/02/2016 3:21 pm
Posts: 20561
Free Member
 

What shape and what position (ie height from floor) is the radiator compared to the old one? If it is higher on the wall and more narrow (so the top of it is higher up the wall) then more heat will be heating the top of your room.


 
Posted : 04/02/2016 3:24 pm
Posts: 0
Free Member
Topic starter
 

How hot though?

Well, so hot that I can't even touch it properly, like a pot handle when it's been in the oven for 10 minutes...

What shape and what position (ie height from floor) is the radiator compared to the old one? If it is higher on the wall and more narrow (so the top of it is higher up the wall) then more heat will be heating the top of your room.

The old one was wider, so the towels ended up side by side on two levels, the new one is narrower with towels on four levels. I'd say that the new one is not significantly higher from the floor, maybe 10cm? But yes, the top of it is very high compared to the old one, so maybe all that lovely heat stays hovering on the ceiling 🙁


 
Posted : 04/02/2016 3:58 pm
Posts: 0
Free Member
 

Yes - it'll work without a TRV on there - you want the water to be going through each rad at the same speed - hence listening for the "shhhhh" noise - turn the lockshield off and then on and you'll know what I mean.


 
Posted : 04/02/2016 4:01 pm
Posts: 41642
Free Member
 

The comment above about TRVs does not apply to most modern systems as the radiator without the TRV should be in the room with the room stat. An old system with a convection loop might have 2 rads without TRVs as one provides active cooling for the boiler (in our case the bathroom) and then another is the return loop for the system (in our case the landing and stupidly we have a TRV in the kitchen with the room stat so I took it off as the place is rented and not mine to mess with any further).

I would check that the system is definitely bled, close off all but one rad at a time and force the water through and check that the towel radiator is definitely getting the proper flow and EVERY bar is getting hot as it could also be an internal fault with the towel rail that you've not noticed.

Didn't know there were different ways of pluming them in, I assumed they all had 2 pipes running in a loop round the house, a bit like the ring main for electrical sockets, then the last one was left open to give the hot water somewhere to go if all the heaters are 'off'. So the boiler churns out hot water until either the thermostat clicks off, and it modulates the heat input to maintain a constant water temp, so when only the towel rail is open it's not running full wack?

Am I going to bugger something up having TRV's everywhere apart from the towel rail?

Some of the rads (specifically the TRV's) make one hell of of a racket when almost closed, I just put that down to them not being quite as bi-directional as the blurb claimed (so the flow is forcing them closed, spring open, flow restarts, etc at about 50hz).

All the lockshields are fully open, the TRV's modulate the flow. Without the TRV you'd use the adjustable valve on the other end to modulate the flow surely, not the lockshield?


 
Posted : 04/02/2016 4:09 pm
 teef
Posts: 0
Free Member
 

Well, so hot that I can't even touch it properly, like a pot handle when it's been in the oven for 10 minutes...

That's a sign it's inefficient and not heating the room - it should be dissipating the heat. Get rid of it and get a proper radiator in.


 
Posted : 04/02/2016 4:11 pm
Posts: 20561
Free Member
 

But yes, the top of it is very high compared to the old one, so maybe all that lovely heat stays hovering on the ceiling

I think that might be your problem then - we replaced two very old 'standard' radiators (not even finned ones) with much higher output vertical ones but we had to do quite a bit of faffing with the balancing before we got them heating the room enough.

That's a sign it's inefficient and not heating the room - it should be dissipating the heat.

Does not make sense - are you saying that a cooler radiator will heat a room more efficiently? Surely if the radiator is hotter more heat gets radiated into the room?


 
Posted : 04/02/2016 4:23 pm
Posts: 0
Free Member
 

There should be a loop.
So even if every radiator is on the boiler can still circulate.
Off that flow/return loop there is a take off for each rad.
Often the TRV gets put on the "wrong" side.
This still allows water into the rad and it gets hot - can also cause the back pressure issues on the TRV's as noted.
The TRV allows the water [b]IN[/b] to the rad.
The lockshield closes the [b]output[/b].
Again - I was taught to turn the heating to max.
Then at each rad - open the TRV fully (or remove the head).
Then close the lockshield.
At this point you open the lockshield again slowly listening for the point it goes silent (or as quiet as it gets).
Once is goes quiet - close the lockshield slowly until you hear a good solid "shhhhhhhhh".
This is now holding the water in the rad and allowing it long enough to convect heat. But not stopping it returning into the circuit.
Repeat this for each rad.
Most people (and loads of plumbers) just wind the valves fully open and then "back a quarter" so the valves doesn't corrode open.
This doesn't match each rad though as the pressure will be different around the circuit as molgrips has found.
In theory you should use a manometer on each one but not as easy as you think for diy.

Teef - if the rad isn't getting hot then it isn't working - so your comment is so bad it's almost not worth commenting on. Basic junior school physics - it needs to take the heat from the water (about 70 degrees centigrade) and radiate that into the air - if the rad isn't hot then it isn't working - if it is hot - the same temp as the water flowing through it then it [b]IS[/b] working efficiently.
The issue here is that the overall temp coefficient of the room has changed.
Large ceramic tiles will take a lot longer to warm to room temp than small ones so for a start it will feel colder underfoot.


 
Posted : 04/02/2016 4:25 pm
 teef
Posts: 0
Free Member
 

Does not make sense - are you saying that a cooler radiator will heat a room more efficiently? Surely if the radiator is hotter more heat gets radiated into the room?

The idea is that the heat is transferred from the radiator to the room - not just kept within itself. A proper radiator is able to perform it's task more efficiently because it has a larger surface area. Think fins on brake pads - they dissipate the heat away from the brakes more effectively due to increased surface area.


 
Posted : 04/02/2016 4:43 pm
Posts: 41642
Free Member
 

But you only need one valve to regulate the flow, TRV's aren't on/off they close gradually so when TRV set point is reached it's still slightly open, but that's academic as they're not calibrated, and that style of valve is very much on/off (you'll get 90%+ of the flow when it's nominally 10% open, so even if the actuator is going from 0-100% it's not doing much util the valve is almost closed).

I get the need to balance the valves when there are no TRV's, but it makes no sense to do it with them fitted to all rads, unless you really want the house to warm up very evenly, rather than the TRV's closing one at a time and the flow finding the next easiest route*.

*it doesn't flow balances so the pressure drops through each route are equal, but the net effect is most will go the easiest way.


 
Posted : 04/02/2016 4:51 pm
Posts: 20561
Free Member
 

The idea is that the heat is transferred from the radiator to the room - not just kept within itself. A proper radiator is able to perform it's task more efficiently because it has a larger surface area. Think fins on brake pads - they dissipate the heat away from the brakes more effectively due to increased surface area.

I get the argument about fins as you get more surface area from which heat can dissipate. But I cannot fathom your argument about a hot radiator not radiating heat. If it is hot it is hot and it will radiate that heat as efficiently as the design allows. Being hotter can't possibly mean it isn't as efficient as if it is running cooler.


 
Posted : 04/02/2016 5:13 pm
Posts: 4421
Full Member
 

I'm afraid that's the case though, Towel rads, especially chrome ones are very good at getting hot locally to heat towels, they're not very good at heating a room however. We have a massive vertical radiator in the living room, and although it looks very nice and gets too hot to touch, the room is always bloody freezing. The other room, exactly the same size which has a std, finned radiator is toasty warm all the time.

I suspect there's not an awful lot you can do about it now shy of swapping the radiator for another type but I guess as you're all tiled up it's a bit late in the day for this.


 
Posted : 04/02/2016 5:23 pm
 teef
Posts: 0
Free Member
 

If it is hot it is hot and it will radiate that heat as efficiently as the design allows. Being hotter can't possibly mean it isn't as efficient as if it is running cooler.

What I meant was that if it's always hot then the heat isn't being dissipated very well. Radiators should be hot when they're raising the temperature in a room and cool down when the required temperature has been reached. A radiator with a larger surface area will perform this more efficiently than one with a smaller surface area.


 
Posted : 04/02/2016 6:05 pm
Posts: 2642
Free Member
 

I get the need to balance the valves when there are no TRV's, but it makes no sense to do it with them fitted to all rads, unless you really want the house to warm up very evenly, rather than the TRV's closing one at a time and the flow finding the next easiest route*.

You need to balance them as if the TRV isn't there so that:

a) You get heat evenly around the house;
b) There's enough load on the boiler to keep it firing until the whole house is up to temperature.

If the flow all whizzes through the first couple of rads and goes back to the boiler, then the boiler will reduce its output / cut off because it "sees" hot water coming back. This will mean that the house takes a lot longer to heat up than it should. [Which I think is what's happening to alp_girl's CH]

There's only so much flow available from the boiler pump, so the rads need to be balanced using lock-shield valves to share it out ('lock-shield' so nobody inadvertently buggers about with the adjustment subsequently). The proper way to do this is to measure the temperature drop between flow and return on each rad and adjust the L-S valve until you get the design figure (12 degrees C?). A heating [u]engineer[/u] will know this.

After that, adjust the TRVs to achieve comfort 🙂


 
Posted : 04/02/2016 6:31 pm
Posts: 1617
Free Member
 

I get the argument about fins as you get more surface area from which heat can dissipate. But I cannot fathom your argument about a hot radiator not radiating heat. If it is hot it is hot and it will radiate that heat as efficiently as the design allows. Being hotter can't possibly mean it isn't as efficient as if it is running cooler.

Think of it another way.

If you wrap a radiator in insulation it will get very hot and the room will stay cold.

As soon as you remove the insulation the heat will be transferred away from the radiator quicker and it's temp will drop. It is then the job of the boiler to keep topping up the heat.

dT is the difference in temp between the source and the sink (not your bathroom sink). The radiator is the source and the room is the sink. In a lossy system like a draughty old house you generally opt for a high dT system like radiators and in a nicely insulated and well sealed house you can go for a low dT system such as underfloor heating. The higher the dT the higher the heat transfer rate will be, which is why you want a high dT in the draughty case but it will mean your boiler will work harder. But that assumes your radiator is efficient at transferring the heat.

Just like the insulation, the design of the radiator affects the heat transfer coefficient into the air. Smooth surfaces, shiny coatings, low actual surface area are all bad in terms of heat transfer. A radiator is designed so that air has to navigate up through fins as it rises due to convention, getting warmer and warmer and a shiny teapot will stay warmer for longer than a black one, if all else is the identical, as the radiative heat transfer is lower also.

towel rails are not designed to heat air effectively so they have a lower BTU output than the equivalent sized radiator. But if if you match the BTU output to that of a smaller radiator that was there then it should be fine.


 
Posted : 04/02/2016 7:24 pm