Cooker electrics
 

  You don't need to be an 'investor' to invest in Singletrack: 6 days left: 95% of target - Find out more

[Closed] Cooker electrics

6 Posts
4 Users
0 Reactions
96 Views
Posts: 843
Free Member
Topic starter
 

Following on from my induction hob question I'm now looking at the practicalities of replacing the hob, and possibly the oven.

Our hob (knackered) is rated at 7.2kw, and our oven (Neff, still going strong) is rated at 5.1kw, this is all on a 30amp breaker with 6mm wiring.

I'm assuming that if I replace with the same wattage or less it should all be good, if so how much wriggle room have I got if the new hob (and maybe oven) have a higher wattage rating? And also, is 7.2kw enough for a decent induction hob?


 
Posted : 29/06/2020 1:05 pm
Posts: 0
Free Member
 

It shouldn't just be the breaker that's 30A, the wiring should be as well and the isolator switch.... so you're running about 2/3rds of 30A.
I can't see the exceeding that but I'd not screw about with that kind of current... (and I screw about with lots)


 
Posted : 29/06/2020 1:33 pm
Posts: 149
Free Member
 

From your post its seems you have the hob and the oven on one 30A circuit, therefore assume
Currently 12300w maximum demand divided by the supply voltage of 230v = 53.4 A

By applying diversity as per IET BS 7671
“The first 10 A of the rated current plus 30 % of the remainder of the rated current plus 5 A if a socket-outlet is incorporated in the control unit”

I have assumed you have no socket outlet.
10A + 30% 0f 43A = 22.9A load after diversity applied

So you have potential of raising the loading but I would try to resist as although 6mm has circa 40A + capacity, this is based on its condition and a well ventilated install (this can be severally curtailed in the cable is with thermal insulation/buried in the wall) 7kw -8kw is more than enough for any kitchen hob.

I hope this helps


 
Posted : 29/06/2020 3:11 pm
Posts: 4421
Full Member
 

7kw -8kw is more than enough for any kitchen hob.

MOST hobs. I'm fitting one in a few weeks at 9.6kw...


 
Posted : 29/06/2020 3:50 pm
Posts: 843
Free Member
Topic starter
 

Thanks spanishfly, that's about what I worked it out at (after reading up on it), I just needed it confirming by someone who knows what they're doing!

The cable is in good condition, and it runs around the eaves so it's in a pretty cool area, but it does run in insulation from the ceiling to the cooker switch (about 5' long). Will that hurt it if I put an extra 0.7kw through it?


 
Posted : 29/06/2020 8:24 pm
Posts: 149
Free Member
 

700w adds 3A prior to diversity, bearing in mind the likely hood of all rings being utilised at max simultaneously is going to me rare (Christmas day maybe....) I would not lose sleep about it.

FYI TW & E 6mm max current capacity clipped direct is 47 A

TW &E Capacity


 
Posted : 30/06/2020 8:47 am
Posts: 843
Free Member
Topic starter
 

Thanks very much. STW is always the best source for electrical info, much better than Lambretta forums or modelling one's! 😀


 
Posted : 30/06/2020 1:24 pm