i have a Bosch Worcester greenstar combi boiler I have a couple of problems with:

When I run the hot tap in the bathroom the boiler works fine for 3 -4 mins then trips out, restart and repeat. It only does this with this ONE hot tap in the house.

Recently when having a shower the hot water has become very twitchy ie it's either scalding hot or freezing cold, all within about 5 mm rotation of the shower mixer.

both faults are in the bathroom which is at the same level as the boiler. Don't know if that makes a difference but thought it might be relevant.

any thoughts anyone? (preferably folk with some plumbing heating knowledge!)

cheers
Khayamolly.


 
Posted : 28/08/2013 5:17 pm
Posts: 4170
Free Member
 

The shower symptoms suggest the mixer may be faulty. I had a faulty shower mixer that allowed cross-flow between hot and cold, even when in the off position, so as soon as I turn off the hot tap, cold water backfed into the boiler. Don't immediately see how that could cause your boiler symptoms but worth checking out - once your system is not working as designed lots of weird things can happen! Fixed by putting non-return valves in the the pipes to the shower (replacing the shower will be done sometime but is a big job as the pipes in the wall are non-standard).


 
Posted : 28/08/2013 5:37 pm
Posts: 0
Free Member
 

Rift in time-space continuam


 
Posted : 28/08/2013 5:56 pm
Posts: 5559
Free Member
 

not sure how it trips out on the hot tap as the temperature is controlled to 58 ish degrees iirc from mine.

I suspect the two are separate faults and mixer sounds like a good one.


 
Posted : 28/08/2013 6:01 pm
Posts: 7167
Full Member
 

Could be a faulty flow rate sensor . Lowish flow = very hot water , sensor then tells boiler tap/shower is off ( when it isnt ) and turns off heat. Water still runs but goes cold.
See if you can recreate this by popping the cover and running a hot tap in the bathroom.
The boiler will fire , and you will see flames, get your assistant to slowly turn down the flow rate. Shout when flames go out , if tap is still running then you have a problem somewhere.


 
Posted : 28/08/2013 7:10 pm
Posts: 0
Free Member
Topic starter
 

thanks all single track mind sounds the mot likely as the shower is only a year old. However I am inclined to agree with dales rider and blame a rift in the space time continuum.
thanks all will investigate