Cold radiator?
 

  You don't need to be an 'investor' to invest in Singletrack: 6 days left: 95% of target - Find out more

[Closed] Cold radiator?

7 Posts
7 Users
0 Reactions
51 Views
Posts: 193
Free Member
Topic starter
 

Seems to have stopped working since yesterday

Entire radiator is cold, and the two pipes supplying it

All other rads are hot

TRV failed?


 
Posted : 01/11/2016 10:15 pm
Posts: 23277
Free Member
 

Sticky TRV? I had to free up two this weekend.


 
Posted : 01/11/2016 10:19 pm
Posts: 193
Free Member
Topic starter
 

Sticky as in won't turn? Seems to turn fine


 
Posted : 01/11/2016 10:20 pm
Posts: 41395
Free Member
 

No, unscrew it and make sure the valve thing sticking out moves.


 
Posted : 01/11/2016 10:25 pm
Posts: 0
Free Member
 

Yup, take the TRV off and try pushing and pulling the pin on the valve with a pair of pliers - apply a wee drop of oil if it's sticky.


 
Posted : 01/11/2016 10:32 pm
Posts: 0
Free Member
 

A per Al's advice above, there should be a small poppet type valve below the TRV plastic top section, unscrew the body of the TRV then using a pair of needle nose pliers carefully try and move the little rod in the center of the valve up and down to free it off.

Also would be worth checking that rad is not full of air. If the heating has not been on and there is a slow leak somewhere it may be that since water has been pumped round the system again all the air has migrated to the 1 radiator.


 
Posted : 01/11/2016 10:36 pm
Posts: 7433
Free Member
 

On a similar topic, how much bleeding should a system need? Ours generally has an empty rad (the only one on the highest floor) at the onset of winter, I usually bleed it a bit during the winter too. Sign of a problem or nothing to worry about?


 
Posted : 01/11/2016 10:58 pm
Posts: 6071
Free Member
 

Sign of a problem or nothing to worry about?

It's certainly not right, but how much of a problem? It depends on the gas that you're bleeding:
Hydrogen sulphide (rotten egg smell) is unusual (and toxic) and is indicative of a bacterial problem
Hydrogen is caused by corrosion in the system and can be associated with a new system or components, e.g. a rad (it can also be long-standing)
Air is often either a leak or a pump problem
If it's not air then draining and using a cleaner/inhibitor in the refill will probably help (e.g. Fernox, etc)


 
Posted : 02/11/2016 6:26 am