Anyone recommend a coating for a bunded blockwork wall around a diesel gen set?


 
Posted : 05/05/2015 1:30 pm
Posts: 7915
Free Member
 

Presumably diesel proof?


 
Posted : 05/05/2015 1:32 pm
Posts: 227
Free Member
Topic starter
 

for sure, looked at Toughseal but it seems damn expensive!


 
Posted : 05/05/2015 1:36 pm
Posts: 0
Free Member
 

Plant room paint? Epoxy I think. Sometimes called tanking. Not sure, so I'd recommend you look into it.


 
Posted : 05/05/2015 1:41 pm
 Sui
Posts: 3107
Free Member
 

You cant use blockwork, it's got to be cast cement. Wall height needs to be adequate to contain 110% of the largest tank capacity as well. How big is this gen set, if it's relatively small (in physical size), it may be easier to buy a polyprop bund for it to sit on. If it's big (i.e. container size job), then ask the manufacturers. Main thing is to have a spill tray at the filling point. Your local fireman can advise as, as any permanent installation where fuel is concerned is supposed ot be signed off - you literally walk into local fire station and ask for the boss and he'll help.


 
Posted : 05/05/2015 1:56 pm
Posts: 0
Free Member
 

GRP job?
I see plenty of commercial gensets in blockwork bunds. They might be cast inside though.


 
Posted : 05/05/2015 1:58 pm
 Sui
Posts: 3107
Free Member
 

Check the Genset first - if the fuel tank is double skinned you wont need a bund, just adequate provision to catch spills on filling. It woudln't surprise me what some places do, but having been involved in a new tank farm being set up, the rules are very prescriptive when they need to be (then not when you really want them to be!).


 
Posted : 05/05/2015 2:02 pm
 Sui
Posts: 3107
Free Member
 

jonesy, if you want some very specific advice i'm happy for you to drop me a mail (in profile) and i'll have a chat with my chief engineer on plant.


 
Posted : 05/05/2015 2:07 pm
Posts: 227
Free Member
Topic starter
 

Looking through the regs a blockwork on seems fine, needs 15mm render to inside face. It's the sealant/coating onto this I need to suss out, ECS, Vandex etc etc


 