Air Source Heat pump and solar to replace oil boiler

64 Posts
34 Users
12 Reactions
1,083 Views
Posts: 40
Free Member
Topic starter
 

I’m looking for some advice regarding what to do about the almost 30 yr old oil fired boiler in my house.

It is not without its flaws and I’m reluctant to wait till it dies and then have to rush into repair/replacement (inevitably in the depths of winter!) so I’ve recently looked into the costs of replacing it with an air source heat pump plus a 5.6kw (south facing) solar array and have found an installer I’m happy with, but am in two minds about whether it’ll end up costing a fortune to run!

The house is quite large~270m^2, with underfloor heating on the ground floor and radiators upstairs. Including in the quote is replacement of all rads with larger ones to allow for running both heating circuits at a lower temp, as well as a new hot water cylinder.

Does anyone have any experience of making a similar change? Or can anyone point me to a simple way of using the fact that I tracked oil consumption last winter to estimate how much it might cost for a similar amount of heating from an air source system??

 
Posted : 01/07/2023 7:03 pm
Posts: 39449
Free Member
 

Any insulation ? It's going to cost lots to run. The insulation will lessen the blow.

 
Posted : 01/07/2023 7:42 pm
Posts: 8612
Full Member
 

Out of interest why air source and not ground source? I was under the (possibly mistaken) impression that ground source just involved a borehole now and was better in winter as the ground is always above freezing a few feet down.

 
Posted : 01/07/2023 7:49 pm
Posts: 1113
Full Member
 

Air source and ground source only are really worth installing in new very well insulated homes, they very rarely are a wise choice in older properties

 
Posted : 01/07/2023 7:49 pm
Posts: 39449
Free Member
 

Out of interest why air source and not ground source?

Cost I'd imagine.

 
Posted : 01/07/2023 7:57 pm
Posts: 3000
Free Member
 

Similar here, I had an epc done so asked the assessor what he thought about an air source heat pump.  Only good on new builds, I d have to spend so much on insulation, new rads it's not worth it.

House has access to under floor so he did say get that insulated, as well as more in the loft.

Don't know if they are still doing it but Skipton building society were doing epc s for free, no catch, if so just open an account with a quid and get one.

 
Posted : 01/07/2023 7:58 pm
Posts: 3754
Full Member
 

Ground source either need a 10m bore hole(s) or large enough ground area for a series of trenches if you can't go vertical - neither option is cheap.

Air source are great until you get to around/below freezing then the efficiency massively reduces - less than 1:1 when going into defrost cycle.

Plus you'll need newer bigger rads (about 30% bigger) as the system runs at a lower temp than a boiler.

You could offset with solar PV and battery storage - but not going to be cheap.

 
Posted : 01/07/2023 8:03 pm
Posts: 40
Free Member
Topic starter
 

House was built in 1996 and is quite well insulated in theory (cavity wall insulation, triple glazing, >200mm loft insulation) but I spent last winter (our first in the house) chasing drafts where things weren’t quite right (gaps around some exposed timbers, flush spotlights fitted in a pitched roof), so while it’s not a period property with leaky sash windows, it’s not perfect!

Putting aside the variability of the solar, is it possible to convert the quantity of oil used last winter to an equivalent energy input and figure out how much the same amount of energy input from a heat pump would cost for a given electricity price? Or does the varying efficiency as external temps drop make that too complex a set of equations for a meaningful comparison?

 
Posted : 01/07/2023 8:06 pm
Posts: 39449
Free Member
 

Trying to offset electric heating with solar PV in the UK would be like throwing a sausage up sauchiehall street.

Some of the numbers being quoted by air pump users on the PV forums are eye watering.

My old man has 8kw of solar PV tracking the winter sun and he is in the middle to south of France and it doesn't even touch the sides with his air source heat pump and the 2 thermodynamic tanks

 
Posted : 01/07/2023 8:07 pm
Posts: 3149
Full Member
 

I understand that air to air heat pumps are very efficient but they only provide heating and require a separate hot water solution

 
Posted : 01/07/2023 8:09 pm
Posts: 3754
Full Member
 

@trail_rat that's why I suggested battery storage (but you'd need a lot!).

Whoever told the government that air source heat pumps are the way forward wants shooting.....

As said better for new homes but still not all it's cracked up to be.

We generally advise clients if they have gas to their property to keep going with it - you can cheaply swap the burners when it changes to hydrogen mix.

With oil or tanked gas it's a bit of an awkward one.....

 
Posted : 01/07/2023 8:17 pm
Posts: 3754
Full Member
 

@dc1988 they're efficient as long as there is heat to take out of the air.

The less heat it can extract the more it has to put in via the electric heater.

Typically they quote about 3:1, but as you get closer to and below freezing then it's pretty much 1:1 as the heater is doing all the work.

You can get heating & hot water - Mitsubishi do a combined system. It still requires an immersion heater though in the cylinder same as a conventional system.

 
Posted : 01/07/2023 8:25 pm
Posts: 7932
Free Member
 

I enquired with a company that installs heat pumps with the view to replacing the 15-year-old oil boiler in my house.

Conclusion was that it’s possible but expensive, and if I wanted to do it on environmental grounds then changing to HVO is a much better bet.

With batteries you can shift most of your energy use to off-peak times (so purely resistive heating of hot water, and some use during the day).

Do not expect anything realistic from solar in the winter months. Mine covered hot water from March - November but the batteries were being topped up from the grid to handle everything else.

 
Posted : 01/07/2023 8:26 pm
Posts: 10539
Full Member
 

£22000 to replace our oil boiler with ASHP for including all the required conversion to 15-22mm pipe work. That doesn’t include the costs to re lay the floor, sort everything out.

Crikey.

 
Posted : 01/07/2023 8:26 pm
peesbee reacted
Posts: 2006
Full Member
 

but as you get closer to and below freezing then it’s pretty much 1:1 as the heater is doing all the work.

This is just not true. There is still plenty of heat in the air, just because it's gone below the temperature at which water freezes doesn't change much. Your freezer wouldn't work otherwise, that's extracting heat from -18C.

At low but above zero temperatures it can require an occasional defrost cycle to remove frost buildup. As it goes below zero it shouldn't need to defrost as much or at all because there's less moisture in the air to freeze. The SCOP of a properly designed system should average above 3 over the winter season. Research has shown they can work in all housing types; the biggest problem is normally finding space to put the outdoor unit. Air-to-air units won't do hot water, but air-to-water systems (ie. radiators) will. Our solar PV couldn't run our A2A units on its own all winter but still provided a worthwhile contribution over the darkest months; in the shoulder months before about November and from about late February they provided the majority of the power needed for all but a few cold, dark days.

Ground source either need a 10m bore hole(s)

Boreholes for vertical GSHPs are normally waaaaay deeper than that, 100m is more likely. They are more efficient as the temperature is more constant but very expensive...

 
Posted : 02/07/2023 12:04 am
Posts: 299
Free Member
 

Our intention is air to water heat pump providing ufh and dhw.

Europe seems to be well ahead of American manufacturers so should be some decent options.

Can be below minus 10deg through the winter for short periods but seems like a reliable solution on the american north west coast

 
Posted : 02/07/2023 12:48 am
dyfidelight reacted
 Bear
Posts: 2311
Free Member
 

Sounds like you’ve got a new build with microbore pipework feeding rads. A real problems as most new build of the last 25 years are like this.
Heat pumps can heat any property the design is critical though. If a building which is poorly insulated  needs 20kw it doesn’t matter which way of delivering it you use it will be expensive and worthwhile exploring some extra insulation.
The problem is if people fit heat pumps to these properties and don’t undertake a proper system upgrade then you are going to struggle as you can’t actually deliver 20kw at the low flow temp required.
It will be interesting to see what comes on the consultation to remove the wholesale price of gas being linked to electricity cost.

 
Posted : 02/07/2023 7:57 am
Posts: 10539
Full Member
 

The general rule of thumb is that for horizontal GSHP, you need 3* the footprint of the house in available land. And for vertical GSHP, you need a number of boreholes, 100m deep equal to 2x the sqm/100 of the house. So my house is 170sqm, I’d need 3x 100*.015m boreholes. My last quotes for this were £19000 just for the boreholes.

 
Posted : 02/07/2023 8:22 am
 Bear
Posts: 2311
Free Member
 

Daffy - that’s too general as the insulation levels could differ hugely.

 
Posted : 02/07/2023 9:14 am
Posts: 10539
Full Member
 

That average was based on current UK housing stock.

Obviously new builds and different parts of Europe will differ. I’m also told that there are difficulties with ASHP that’re if not specific, then at least detrimental to performance in the UK. Average humidity is high, which is why we get wet snow and ice formation more than other parts of Europe. The humidity can affect the performance of ASHP as the temperature approaches zero requiring substantial input energy for defrost cycles.

 
Posted : 02/07/2023 10:16 am
Posts: 10539
Full Member
 

I want ASHP to work, but in reality, for it to be carbon neutral at the local level, I’d need to double the size of my solar array (input energy) for the winter, somehow install external insulation onto a wall subject to driving rain and high winds, rip up every floor and insulate and replumb, install a 210l unvented tank and electronics for solar thermal, install therma skirt or MUCH larger radiators upstairs and UF heating downstairs.

The price will be close to £35-40k, but I’d also need to find people to do it. It took me almost a year to find a solar guy and a roofer who’d work together on an in-roof solar and re-roof.

 
Posted : 02/07/2023 10:22 am
 IHN
Posts: 19694
Full Member
 

Quick question - why ASHP, and not electric radiators?

 
Posted : 02/07/2023 11:18 am
Posts: 39449
Free Member
 

Quick question – why ASHP, and not electric radiators?

Electric rads 1 unit in = 1 unit out - all of the time .

Ashp has potential for 1 in 3 out some of the time remembering it works on the kelvin scale so as pointed out above there's always "heat" in the air ..... But around here they still plummet to 1:1 in winter

Flip side is - 22grand buys a lot of radiators and electric.

My old man's was installed courtesy of the  gov due to them being in hospitality. It was not 22grand. It's more expensive than the oil it replaced

 
Posted : 02/07/2023 11:23 am
Posts: 4643
Full Member
 

Boreholes for vertical GSHPs are normally waaaaay deeper than that, 100m is more likely.
</blockquote

Was gonna say this, my parents have just had three 230m bores sunk for their gshp install. It’s feeding a 25 year old, very well insulated 460m^2 house in northern Donegal to replace what looked like a small steam tugboat boiler.

Their heat store is amusing

 
Posted : 02/07/2023 11:37 am
Posts: 10539
Full Member
 

Do you happen to know and could you disclose what they paid for those holes?

 
Posted : 02/07/2023 11:50 am
Posts: 3265
Full Member
 

OP have you checked out https://protonsforbreakfast.wordpress.com

I’m expecting we’ll make a change to an ASHP sometime soon. I do not expect to save any money in running an ASHP. I do expect to eliminate our dependency on gas.

GSHP would be an interesting, yet expensive, option if we were in an empty area with land. Not an option with a mature garden and city-edge living.

 
Posted : 02/07/2023 11:58 am
Posts: 3351
Full Member
 

When considering the future, I assume it's a given that oil and gas will continue to get more expensive (as a general trend) and for alternatives to work electricity needs to get cheaper (relatively)?

Also burning any alternative hydrocarbons is surely only a interim solution?

 
Posted : 02/07/2023 12:33 pm
 Bear
Posts: 2311
Free Member
 

ASHP will be better than 1:1 in winter, or should be with the correct design.
As someone has said it is the humidity at low temp that kills the efficiency compared to scadanvian countries

 
Posted : 02/07/2023 2:03 pm
Posts: 265
Full Member
 

Heatgeek on YouTube is worth a watch about gshp and ashp along with other alternatives.

https://youtube.com/@HeatGeek

 
Posted : 02/07/2023 3:16 pm
Posts: 91000
Free Member
 

My sister just had ASHP installed for free via a grant. There's no gas in the village and the 90s house didn't have any central heating, relying on a wood burning stove and storage heaters which were of course crap. The new radiators are huge as are the pipes, so let's hope the insulation is good enough.

 
Posted : 02/07/2023 3:28 pm
 mert
Posts: 3831
Free Member
 

My in laws got a brand new GSHP a couple of years ago. One borehole, i *think* 12cm dia and 120m deep. That replaced a pellet burner (with electric boost on the tank), which in turn replaced an oil burner that had been in since jesus was a young man. It's about 120sqm house, built in the 1880s and insulated with wool and straw with asbestos cladding... It leaks like a sieve. They paid a little over 25k (about 2/3rds for the drilling), heating bills are less than half now. And FiL doesn't have to clean the burner out and empty the ash tray anymore.

Mine is a 130mx15cm borehole (i've got the original receipt), that heats my well insulated 200sqm house (triple glazed, 300mm insulation in the attic, heat reclamation system in the attic) "adequately". It needs a bit of a top up when it gets below about -10 outside. It was installed in 2001, so the price is irrelevant! Biggest issue is the radiators weren't replaced, so it's still got the small ones designed for high temperatures.

Also, we've got 4 or 5 local companies that are bidding for drilling/installation work. Whereas you guys in the UK will have a much more limited list i guess!

BTW This is in sweden, where minimum standards for insulation are a lot higher and GSHP/ASHP has been mainstream for years.

 
Posted : 02/07/2023 3:33 pm
Posts: 91000
Free Member
 

Fitting larger rads is easy though, if you have the space. I've done one, I'll do a couple more this winter.

 
Posted : 02/07/2023 4:07 pm
Posts: 10539
Full Member
 

Large rads is easy, but large pipe work isn’t.

 
Posted : 02/07/2023 4:16 pm
 mert
Posts: 3831
Free Member
 

Easy but expensive, i've got 14 of them still to do.

 
Posted : 02/07/2023 4:17 pm
Posts: 4643
Full Member
 

Boreholes were £10240.

Drilling rig was amusingly small. 

 
Posted : 02/07/2023 4:25 pm
Posts: 2586
Free Member
 

This is something I do know about.

Ground vs Air. Ground costs a fortune to fit, around £10k extra for the boreholes. Then there is the problem that the heat from the ground is sucked out, and not replaced quick enough. It has been known for the ground around the bore to freeze, as the heat transfer undergound just isnt fast enough to replenish the heat taken by the pipes.

ASHP benefit in the Uk from an air tempertaure that doesnt go below 5 degree c for something like 90% of the time. (OK, the Cairngorms get more cold days, but in general, over the UK,the air stays above freezing for most of the time, and above 5 degrees for 90%+). The COP in Summer months for heating the water can be as high as 6, the ground source will still be at 10 degrees in July, so a COP of 3+ could be expected.

Insulation/older houses and other fallacies. It is untrue. A HP can be fitted in any premises,and should be roughly equivalent in running costs to a gas boiler (obviously gas and electric prices differentials affect this, but it has stayed typically a price of 3:1 for a while now). The COP should be 3 or more. More will make it cheaper to run than a gas boiler, and certainly cheaper than an oil boiler. Insulation, of course insulation helps. It helps whatever heat source you have. If your heat loss from the house is 10kW, it’ll be 10kW whether its gas, oil or electric that heats it.

Larger radiators and piping is required. Not always. My CH is 30+ years old. I tried it last year by running the gas boiler at a flow temperature of 35 degrees. It was toasty as ever, and in running at the low temperature, it made my gas boiler more efficient, as it wasnt cycling as much, and condensing at all times it ran. A HP would be a straight fit in, I have standard single panel rads and 15mm pipework in a 3 bed semi. No change in eithe ris required.

Install cost is the killer, though, it is coming down. A straight swap of a gas boiler can be done for less than £2k, a HP will be likely £6k+ There are some right cowboys out there now fitting them, mainly as the Govt. put up the £5k subsidy, but I doubt the householder will see much of that, the installers are taking the bulk, by increasing their install charges. This has been complained about a lot in the Trade, as to claim the £5k you need to be MCS registered, and it is not easy, cheap or quick, for a Sole Trader to achieve the MCS registration, thats why larger Companies are promoting themsleves so much, sending out Fitters who have not had the relevant training, and the HP is never going to be running properly or at its most economical.

The Industry are aware of this, and MCS are consulting now to reduce the burden in being a Member of their scheme. There are 3rd Party Companies who will apply for the MCS for you, but the typical cost is £1800+, just for them to process the paperwork, adn claim the £5k.

Oil boilers, IIRC, they are not allowed to be fitted new (or replacement) after the end of this year. Yes, thats right, so if you want a new one, get on it quick, or you’ll never get a new one fitted.

 
Posted : 02/07/2023 6:23 pm
prettygreenparrot, phiiiiil, footflaps and 1 people reacted
Posts: 39449
Free Member
 

Boreholes were £10240.

Drilling rig was amusingly small.

Generally a geotechnical unit .

My neighbour hit granite cap and had to go to 300m. The unit they had to bring in cost more on hire than the original total install cost .....

 
Posted : 02/07/2023 7:31 pm
Posts: 40
Free Member
Topic starter
 

Thanks for all the replies.

To answer a couple of queries:

No microbore pipes in the house (one of the things I checked before buying), so the larger rads are all that would be needed upstairs and are already included in the quote I’ve had.

Air source over ground source is indeed a cost thing, I’ve had a quote I consider reasonable for the solar plus air source and all required upgraded rads/hot water tank.

im not too worried about the installation cost, but I’m very interested in how much it’ll end up costing to run… I can swallow the up front costs, but not if it’ll double my heating bills going forward!

 
Posted : 02/07/2023 7:57 pm
Posts: 490
Full Member
 

@alanl that was really insightful, thank you. Reading this wondering what we will do (oil, mid 2000’s stone built house).   Oil boilers not being available post 2023 is a bit scary. Albeit we replaced ours 18 months ago. So should have some time.

 
Posted : 02/07/2023 8:31 pm
 Ewan
Posts: 4336
Free Member
 

Oil boilers not being available post 2023 is a bit scary

Good job it's not true! I've been following this closely and have seen nothing of the sort. There was a consultation but no decision as far as I can tell. The earliest was like 2025 in any event.

 
Posted : 02/07/2023 8:48 pm
tillydog reacted
Posts: 3588
Full Member
 

We're 18 months into ashp on a new build. Numbers are as follows:

4 bed, 130m², 2 to 4 occupants (includes energy hungry teens), everything apart from car on electricity. Total house consumption was 6500 kWh for the first 12 months including a few weeks down to -10C in an exposed windy spot.

Always comfortably warm. Regular mostly 15mm pipework. Rads are pretty standard, just double panel with convector fins. I don't have a measure of the exact efficiency / energy split but it still ran extracting energy at -10 and doesn't do excessive defrosting.

Overall we've been very pleasantly surprised - really thought we'd struggle coming from 25 years of gas combi. The only caveat is you have to drive it properly - ie low and slow not on / off.

I do wonder if ashp theft will become a thing - it has external isolator switch and valves, so would be very easy to disconnect.....

I also know someone that bought a second hand gshp at a very good price - the original owner / install got it wrong so it extracted all the adjacent ground heat faster than it could replenish in winter.

 
Posted : 02/07/2023 8:50 pm
Posts: 2586
Free Member
 

Good job it’s not true! I’ve been following this closely and have seen nothing of the sort. There was a consultation but no decision as far as I can tell. The earliest was like 2025 in any event.

Just googled it, it’s been put back to 2026. I dotn follow it as I’ve never fitted or been interested in oil boilers.

https://www.theecoexperts.co.uk/boilers/oil-boiler-ban

 
Posted : 02/07/2023 9:02 pm
 core
Posts: 2769
Free Member
 

Unless you've got lots of (good) insulation, an ASHP is likely to cost A LOT to run the heating for a house of that size, even with solar PV. The upside is that you've already got UFH, that seems the most efficient way to heat with an ASHP.

They're OK on new builds (better with MVHR) with solar PV. Even then, they take a lot of balancing, need to run at a fairly constant temperature, be programmed well to ramp up/down slowly, and you're best off with a secondary heat source if you want a quick boost as they'll eat electricity trying to affect a big increase.

EPC's are pretty useless if they're produced in RdSAP - the Rd stands for reduced data and means they have even more assumptions in them than proper EPC's that come out the back end of a full SAP calculation, as in the case of a new dwelling.

 
Posted : 04/07/2023 9:40 am
 DrJ
Posts: 13416
Full Member
 

My neighbour hit granite cap and had to go to 300m. The unit they had to bring in cost more on hire than the original total install cost …..

@trailrat You're in O&G, no? Couldn't you have got it done at mates rates?

More helpfully - Octopus will do a survey to tell you how your house measures up in terms of insulation pipework etc and what size HP you would need. Not sure `i totally believe what they say, but it's a place to start.

 
Posted : 04/07/2023 9:50 am
Posts: 7433
Free Member
 

So long as your radiators are big enough there's no reason for ASHP to ever cost more than other methods such as gas. Assuming electricity/gas price ratio stays much the same, and you get something like 3:1 return from the ASHP versus 80% efficiency (ish) from gas. What kills ASHP efficiency is having to run radiators very hot if they are under-sized for the demand (which depends on insulation of course). Gas will be able to run smaller radiators without such an efficiency loss.

Some friends locally have ASHP in an old cold stone house and are very pleased with it. Their radiators are big enough.

 
Posted : 04/07/2023 9:53 am
Posts: 2642
Free Member
 

can anyone point me to a simple way of using the fact that I tracked oil consumption last winter to estimate how much it might cost for a similar amount of heating from an air source system??

Oil (kerosene) is just under 10kWh per litre. An old boiler is probably only going to be ~70% efficient, so your heating input will be something like 7kWh per litre of oil used.

Not an ASHP expert, but I'd expect *a similar heating input* would require, very roughly, 1/2 to 1/3 of the kWh.

As of June 2023, average costs are as follows:

kerosene (with a modern, 90% efficient boiler): 6.75 p/kWh
ASHP (2.7 CoP): 14.23 p/kWh
Mains Gas (DD rate): 11.06 p/kWh

Sauce:
https://nottenergy.com/resources/energy-cost-comparison/

 
Posted : 04/07/2023 10:14 am
Posts: 30093
Full Member
 

As someone has said it is the humidity at low temp that kills the efficiency compared to scadanvian countries

I do wonder if ashp theft will become a thing – it has external isolator switch and valves, so would be very easy to disconnect…..

For UK use to really take off, we need these in the attics. So much housing stock with little external walls to mount on (victorian terraces etc), and many of those that are will be low, damp, too easily accessed from the street, and in the way. Need more UK focused development, rather than importing set ups that work elsewhere.

 
Posted : 04/07/2023 10:17 am
Posts: 7167
Full Member
 

Mates got a 2kw in new build. It heats the entire house. Has ufh and mvhr and a log burner for back up. 260sq mtr but. Its got 150mm insulated walls, insulation in the pad, triple glazing etc.
Still not cheap, but backed witj solar and a decent battery i can see how cheap it could be. Massive front end loading though

 
Posted : 04/07/2023 10:33 am
Posts: 2642
Free Member
 

Just done the maths on the figures in my post above (too late to edit):

If you don't change anything else, ASHP will be ~64% more expensive to run than your current oil boiler; a new oil boiler will be ~28% cheaper to run than your current oil boiler.

 
Posted : 04/07/2023 10:33 am
Posts: 40
Free Member
Topic starter
 

Thanks for this, exactly the kind of order of magnitude comparison I’d not managed to make yet!

After the feedback above I’ve already started ringing around to see if I can find someone willing/able to quote for a replacement, modern oil boiler, no luck yet, but there’s still time to beat the ban if it looks like the best option, particularly if future conversion to HVO looks straightforward…

 
Posted : 04/07/2023 10:44 am
tillydog reacted
Posts: 3588
Full Member
 

You wouldn't put an ashp in the attic because:

Noisy.

It blows out a VERY cold breeze - so you just quickly get a cold attic with restricted ingress of fresh air to extract heat from.

Even if it exhausts straight outside and only harvests air from the attic, the air in a suitably ventilated and house sealed / floor insulated attic won't be appreciably warmer or drier than the air outside as there is such a high flowrate (so not enough time to heat the attic air from limited solar gain).

The drawing tempered air from the attic only works for positive pressure ventilation where the flowrate is tiny and you can get some limited passive daytime solar gain in autumn / spring.

 
Posted : 04/07/2023 10:46 am
Posts: 30093
Full Member
 

the air in a suitably ventilated and house sealed / floor insulated attic won’t be appreciably warmer or drier than the air outside as there is such a high flowrate

You're thinking new build there, I'm thinking retrofit into existing stock.

 
Posted : 04/07/2023 10:48 am
Posts: 5787
Full Member
 

Very interesting to read all this, as we're 9 months into a renovation/ refit of an old house in Dublin - a complete gut job, basically, of a 150-year old place. ASHP was specced, combined with underfloor/ concrete slab downstairs, radiators upstairs. We're replacing all windows with double glazing, installing internal breathable insulation, roof insulation too. And we'll have a wood burner in the living room downstairs.
The consensus is... mixed. ASHP zealots say it'll be amazing, so much cheaper to run than anything else and will always keep us warm. Sceptics say we'll be cold in winter; and nobody is able to say "look, on the one hand x but on the other y" to allow us to make an informed decision.

Ultimately, Irish regs mean we probably have to hit a certain energy rating for the finished house, and ASHP helps with that. But fingers crossed it does what we need!

 
Posted : 04/07/2023 11:09 am
Posts: 39449
Free Member
 

You’re thinking new build there, I’m thinking retrofit into existing stock.

Yes but your still trying to put an ASHP into an attic space. That's the issue regardless of new vs old.

Asside from the vibration/noise. You'd have to feed and vent the condenser in such a way that it believed it was outside otherwise you'll be trying to extract heat from the cold ejected airs

 
Posted : 04/07/2023 11:54 am
Posts: 3265
Full Member
 

Lots of FUD about ASHP about.

One of the reasons I like the protons for breakfast posts is that the poster focuses on simple things:
How much energy do you need to heat your house?
How much energy do you need to consume to provide that heat?

The rest is arithmetic.

Like EVs, I would not pick an ASHP with the intention of saving money. But I would pick one to reduce my fossil fuel burning and local pollution.

subsidies for burning fossil fuels could be with us for a while. https://www.iea.org/commentaries/the-global-energy-crisis-pushed-fossil-fuel-consumption-subsidies-to-an-all-time-high-in-2022

 
Posted : 04/07/2023 12:04 pm
kelvin reacted
Posts: 30093
Full Member
 

You’d have to feed and vent the condenser in such a way that it believed it was outside otherwise you’ll be trying to extract heat from the cold ejected airs

Well, obviously you'd need to vent to the outside. Cold air leaving through a vent rather than the CO2 leaving it from my gas boiler is fine with me. Not looking at air tight purpose built detached homes here, more the rest of us that'll be stuck burning gas for decades to come without air source being engineered to work in existing British housing stock.

But I would pick one to reduce my fossil fuel burning and local pollution.

This.

 
Posted : 04/07/2023 12:16 pm
Posts: 10539
Full Member
 

Like EVs, I would not pick an ASHP with the intention of saving money. But I would pick one to reduce my fossil fuel burning and local pollution.

Like you, I would also do this, but £20k-£40k to install it and then having to pay more to run it, doesn't help to sell it, does it?

The government needs to do something to help this.  They're removed EV subsidies except for tax dodging businesses, there's no environmental subsidies worth speaking of, but we'll happily invest £30-60bn in Hinckley point to reduce our carbon footprint and secure energy.

 
Posted : 04/07/2023 12:56 pm
kelvin reacted
Posts: 3265
Full Member
 

It’s clear where UK government interests lie from their actions.

https://amp.theguardian.com/us-news/2019/may/13/the-planet-is-on-****ing-fire-bill-nye-is-getting-angry-about-climate-change

 
Posted : 04/07/2023 1:03 pm
 mert
Posts: 3831
Free Member
 

Like you, I would also do this, but £20k-£40k to install it and then having to pay more to run it, doesn’t help to sell it, does it?

TBH, it's a gamble isn't it. How much will your conventional CO2 emitting fuels go up in price by, how much of them will your electricity producers use to make your electricity. What will the comparative costs be next year, or in 5 years.

Thing is, if you don't get in now, it might be too expensive to get in later. Like i should have got solar when i had the first quote 6 years ago, the increases in electricity prices would have paid for it by now (instead of the 7-9 years they quoted) that extra chunk of cash I'm now paying for my electricity means i can't put stuff aside for solar, and round here solar installation costs have doubled as well, so i'm falling further behind.

Thankfully i have GSHP, so heating isn't too expensive!

 
Posted : 04/07/2023 1:28 pm
 5lab
Posts: 7921
Free Member
 

on the CO2 side - whilst the mix of electricity in the UK varies, more often than not if I consume more electricity (say to heat my house), isn't that increase in electricity need most likely to be met by non-renewables? So whilst the overall mix might be 70% renewables, the marginal mix is far heavier on the fossil side (you might throw a couple more lumps of coal into a power station, you can't make the wind blow harder), thus making the co2 argument a bit tougher?

 
Posted : 04/07/2023 1:35 pm
 mert
Posts: 3831
Free Member
 

Unless it makes the business case to build more wind turbines a bit more robust, cos coal is 4 quid a lump.

 
Posted : 04/07/2023 1:43 pm
Posts: 30093
Full Member
 

Domestic stuff can only really work if we ramp up renewables at the national level, at speed. But, as it happens, everyone I know who can afford an air source heat pump have had solar fitted at the same time. Grid only supply when dumping oil/gas is probably a big mistake, but that also means the upfront costs are even higher.

 
Posted : 04/07/2023 1:46 pm
Posts: 4954
Free Member
 

At low but above zero temperatures it can require an occasional defrost cycle to remove frost buildup. As it goes below zero it shouldn’t need to defrost as much or at all because there’s less moisture in the air to freeze

I think this is the issue for the UK as this close to zero range with high humidity (so lots of frost) is a common temperature range, better off in colder climates which may initially seem unintuitive until you consider this fact.

 
Posted : 04/07/2023 1:49 pm
kelvin reacted
Posts: 1130
Free Member
 

Larger radiators and piping is required. Not always. My CH is 30+ years old. I tried it last year by running the gas boiler at a flow temperature of 35 degrees. It was toasty as ever, and in running at the low temperature, it made my gas boiler more efficient, as it wasnt cycling as much, and condensing at all times it ran. A HP would be a straight fit in, I have standard single panel rads and 15mm pipework in a 3 bed semi. No change in either is required.

I did a similar experiment last winter.  Running my gas boiler at a 50 degree flow temp, as a heat pump would at the high end.  1928 house, solid walls, double glazing, 300mm loft insulation, and radiators that were sized for a 75 degree flow temp.  Heat loss calculations say the house needs 12kW but I think it's more likely 10.  Heaven knows how old the pipework is.  After only changing two rads for double panel double convector, rather than singles, it was absolutely fine, and saved loads of gas.  Basically, the trick is to run the heating at a lower flow temperature for longer.  Avoids it overshooting, and means the boiler can work more efficiently.

Going to try going lower on the flow temp this year, so will probably increase the size of a couple more rads that can be done without affecting the rooms they're in.  Not going to be putting a heat pump in in the near future (in fact about to install a new gas boiler), but wanted to know the house is capable of it and a 3 to 4kW heat pump would do the trick fine.

 
Posted : 04/07/2023 2:46 pm
kelvin reacted
 ajc
Posts: 212
Free Member
 

This has all the answers. Well 50 of them anyway. Including why you can’t put a heat pump in the loft.

https://www.amazon.co.uk/things-need-know-about-pumps-ebook/dp/B0B1LHF2QG

 
Posted : 04/07/2023 6:59 pm